[EnergyPlus_Support] Re: AirTerminal:SingleDuct:VAV:NoReheat



I have verified that i cannot create a AirTerminal:Singleduct:VAV:NoReheat to get zone temperatures in between 20/25 ºC. I have to define a controller to the heating and cooling coils (both water) of the air handeling unit then that makes me define setpoint air temperatures of the air entering the zone. 
Even if i delete the heat coil controller, the zone temperature in winter does not reach 20ºC.

Basically I want to simulate an Air Handeling Unit with pre-heat, cooling and heating coil (all water), mixing box and a variable fan. No terminal reheating.

What option must i choose? 
Air:Terminal:SingleDuct:Uncontrolled?? if i choose this i think i cannot define de airBranch;
Or should i look into NaturalVentilationAndDuctLeakage for the system? but this does not allow the choise of a variable fan.


Thank-you


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Sounds like you need to include a heating coil in the air loop when 
> using AirTerminal:Singleduct:VAV:NoReheat. I you already have one then 
> you are not controlling it correctly or the zone loads are so diverse 
> that some will wind up below 20C. This can sometimes be corrected by 
> balancing the air loop flow rates to each zone (i.e., giving more flow 
> to colder zones and less flow to warmer zones).
> 
> The supply air reset schedule is used to minimize heating energy in 
> winter. If you kept the same cold supply air temperature all year 
> around, the heating coils would have to work harder in the winter.
> 
> On 3/24/2011 5:47 AM, vieira.jose99 wrote:
> >
> > AirTerminal:SingleDuct:VAV:NoReheat
> >
> > I have set up everything, but I want the mean air temperature to be in 
> > between 20 and 25ºC. But this does not happen. I have the thermostats 
> > configured to be 20/25ºC.
> > The mean air temperature just stays a few degrees above the outside 
> > air temperature.
> > I have the coils, boiler and chiller on autosize.
> >
> > When I configure the same setup to AirTerminal:SingleDuct:VAV:Reheat 
> > with reheat coils on autosize, I get it to be in between 20 and 25ºC.
> >
> > Any advice?
> >
> > Also....can someone explain what is the "Seasonal Reset Supply Air 
> > Temp Sch" for? I have read the inputoutput, but still cannot 
> > understand the basics of this schedule.
> >
> > thank-you
> >
> > 
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/