Zeynep,
I hit this same limitation for window shades. The approach I took was to discretize the window into 10 pieces. In that way, having the shade closed on one of the smaller windows was equivalent to have the shade closed by 10%. I'd imagine you could take the same approach for natural ventilation.
Liam
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, zeynep arsan <arsanzeynep@...> wrote:
>
> Hi,
>
> I should simulate summer natural ventilation of a monitored building. There is a
> set of two summer months data about the glazing area opens in %. Yet, there is
> no fixed area, in other words, the area opens differs per hour. For example, the
> window is opened for 20% between 09:00 and 11:00, for 50% betwen 11:00 and
> 14:00, and else.
>
>
> How can I use scedules to model different glazing area option related to per
> hour? Is it possible to control the opening area with schedules? May I enter
> intermediate fractional values, e.g. 0.2 for 20%, besides to 0 and 1?
>
> Many thanks,
>
> Zeynep Durmus Arsan
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/
=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17190)
http://www.pctools.com/
=======