The ZoneMixing object is for this.
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Karen Walkerman
Sent: Monday, March 28, 2011 11:29 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Transfer Air in Energy Plus
Hello,
I'm modeling a building where there is bathroom exhaust in the core zones which is made up with transfer air from the perimeter zones. Is there a simple way to set up zone transfer air, or do I need to set up airflow network objects for the ventilation system supply and exhaust distribution?
Thanks,
Karen