RE: [EnergyPlus_Support] Modulation of openings in Airflow Network
Omar:
The zone temperatures used to check window or door openings are the values at the previous time step. You may use report frequency ?Detailed? to see what happens. The zone temperatures at the current time step are calculated based on window openings, if the temperature difference between the zone temperature at the previous time step and Tset determines to open a window.
Hope this helps.
Lixing Gu
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of omarvelling
Sent: Friday, April 15, 2011 4:16 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Modulation of openings in Airflow Network
Hi all,
I'm trying to modulate, or to be precise, cancel the modulation of the opening size of an AirflowNetwork:Multizone:Surface object so that it can either be fully open (i.e. Multiplier equals 1.0) or closed i.e. (Multiplier equals 0.0) depending on the ventilation control mode. I have managed to achieve this when the ventilation control mode is set to 'Constant' by specifying a venting availabilty schedule. However, when using 'Temperature' as the ventilation control mode and by setting the Ventilation control zone temperature setpoint at 22 C I found that the output for the 'Window/Door opening factor' is greater than 0.0 even when the zone temperature is below 22 C, that is when Tzone < Tset indicating that the window is partially open. As shown below, I've tried to overcome this by setting the minimum venting opening factor field in the AirflowNetwork:Multizone:Zone object to 1.0. I've also set the two sets of Opening factor Data in the AirflowNetwork:Multi
Can anyone tell me why this is happening?
Thanks in advance,
Omar
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=19888/stime=1302902820>
Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmYTQxOTFkBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzMDI5MDI4MjA->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJka2ZrZnM0BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzAyOTAyODIw>Visit Your Group | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe
__,_._,___
=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320)
<http://www.pctools.com/?cclick=EmailFooterClean_51>http://www.pctools.com
=======