[EnergyPlus_Support] AHU with plate heat exchanger and no mixing box, possible?



Dear All,

I am modelling an AHU with a plate heat exchanger an no mixing box.
It seems that this is not possible in E+ and that I must have an OutdoorAir:Mixer object in the AirLoopHVAC:OutdoorAirSystem:EquipmentList.
Can anybody confirm this limitation?
This is the error that I get:

   ** Severe  ** OutdoorAir:Mixer for AirLoopHVAC:OutdoorAirSystem AHU1_OUTDOOR_AIR_SYSTEM not found.
   **  Fatal  ** GetAirPathData: Errors found getting AirLoopHVAC
  


I tried a workaround, having the OutdoorAir:Mixer and imposing a Minimum Fraction of Outdoor Air Schedule constanly equal to 1.
But this lead to the follwoing warnings:

** Warning ** HeatExchanger:AirToAir:SensibleAndLatent "OA HEAT RECOVERY 1":  Average air volume flow rate is <50% or >130% warning continues. Air flow rate ratio statistics follow.

** Warning ** HeatExchanger:AirToAir:SensibleAndLatent "OA HEAT RECOVERY 1":  Unbalanced air volume flow ratio exceeds  2:1 warning continues. HX flow ratio statistics follow.

Is there any better solution to this issue?
I would kindly appreciate anyone's help on this.
Kind regards,
Andrea



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320)
http://www.pctools.com/
=======