RE: [EnergyPlus_Support] ZoneVentilation Volume Standard Density vary



Robin:

I think you may use one of two output variables to report volume flow rates:

HVAC,Sum,Zone Ventilation Volume Flow Rate Current Density [m3/s]
HVAC,Sum,Zone Ventilation Volume Flow Rate Standard Density [m3/s]

It was found as a bug to report volume flow rates and was fixed for the next
release. It is a report error and has no impact of simulation results.

Lixing  

-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of rgen1202
Sent: Wednesday, May 04, 2011 11:56 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] ZoneVentilation Volume Standard Density vary

Hello,

I have a question about the ZoneVentilation DesignFlowRate.When I set the
Design Flow Rate to a constant value (assuming 0.086162 m3/s, for a single
zone), I don't understand why the output variable Zone Ventilation Volume
Standard Density (hourly) is varying. Can someone explain it? I have checked
the settings and I have all minimum and maximum temperature setted to
default value (this mean no shutoff of ventilation) , the maximum wind speed
is 40 m/s (no shutoff) and only the constant term coeeficient is set to 1,
the other are to 0. Of course, I have tested this setting for a single zone,
without any infiltration or other air system.

Thanks in advance.

Robin GENOUD



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to
energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a
high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
Documentation link and press the "search" button.
Yahoo! Groups Links







------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/