I would set up an HVAC system that can maintain both temperature and humidity. Make sure you can maintain both set points for all simulations. Then use the predicted load variables to calculate Load SHR. You can do this by zone, or sum these values for the entire building.

Output:Variable,*,Zone/Sys Sensible Load Predicted,Hourly;
Output:Variable,*,Zone/Sys Moisture Load Rate Predicted,Hourly;

You will need some additional math for this.

For example, a spreadsheet calc may look like this:

IF(Zone/Sys Sensible Load Predicted < 0, IF(Zone/Sys Moisture Load Rate Predicted < 0, calculate the Cooling Load SHR,1),IF(Zone/Sys Sensible Load Predicted > 0,IF(Zone/Sys Moisture Load Rate Predicted < 0,calculate Heating Load SHR,1,x))

Remember the psychormetrics of calculating SHR. If heating and dehumidifying, the SHR could be > 1 or < 0. A room air dehumidifier has an SHR close to 2.

Look at the upper left hand corner of this psyc chart.

http://www.heatpipe.com/ProductsServices/forengineers/psychrometric_chart.pdf

On 6/6/2011 9:45 AM, Michael Grant wrote:
 

Hey everyone,

 

I know it’s been a while, but going over this subject again, does anyone know how I can get the annual sensible heat ratio (sensible load/total load) of a building (typical is around 0.7)? I’m trying to study the building’s characteristics through infiltration, occupancy, and solar gains.

 

Thanks,

 

 

Michael Grant, MIT

Engineering | Systemair Inc.

(T) 1-506-743-9500

michael.grant@xxxxxxxxxxxxx

http://www.systemair.net

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Richard Raustad
Sent: April-29-11 10:41 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Total Building Sensible and Latent Energy

 

 

I don't know of any report variables that provide actual total or latent energy provided to the zone.  Those existing report variables are related only to sensible energy provided to the zone and includes more than what comes through the zone inlet nodes (e.g. baseboards, room dehumidifiers, etc.). Also remember that these report variables are only related to the "load" when the thermostat set point is met (i.e., if you provide more or less sensible capacity to a zone than is required to meet the set point, it's not really the load). The "load" related to both the thermostat and humidistat set points can be viewed using:

When a zone thermostat is present:
HVAC,Average,Zone/Sys Sensible Load Predicted [W]
HVAC,Average,Zone/Sys Sensible Load to Heating Setpoint Predicted [W]
HVAC,Average,Zone/Sys Sensible Load to Cooling Setpoint Predicted [W]

When a zone humidistat is present:
HVAC,Average,Zone/Sys Moisture Load Rate Predicted [kgWater/s]
HVAC,Average,Zone/Sys Moisture Load Rate Predicted to humidifying setpoint [kgWater/s]
HVAC,Average,Zone/Sys Moisture Load Rate Predicted to dehumidifying setpoint [kgWater/s]


On 4/29/2011 8:24 AM, Michael Grant wrote:

 

Hey everyone,

 

Is there a place in a model where I can have energy plus spit out a building’s total sensible and latent load?

 

Is my only option under “Output:Variable,*,Zone/Sys Sensible Cooling Rate,hourly;” and “Output:Variable,*,Zone/Sys Sensible Heating Rate,hourly;” ?

 

Thanks,

 

Michael Grant, MIT

Engineering | Systemair Inc.

(T) 1-506-743-9500

michael.grant@xxxxxxxxxxxxx

http://www.systemair.net

 



-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
 
UCF - From Promise to Prominence: Celebrating 40 Years


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___