[EnergyPlus_Support] zone temperature
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
 
- Subject: [EnergyPlus_Support] zone temperature
 
- From: "vbing" <valeba23@xxxxxxxxx>
 
- Date: Tue, 07 Jun 2011 15:23:52 -0000
 
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
 
- Delivery-date: Tue, 07 Jun 2011 09:24:09 -0600
 
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1307460248; bh=8swwMyP8uyauvNxdfMqW/iwSegDPgpfcCkVKTgyWLEY=; h=Received:Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=XvkESDYgUb8tmYFjZT/0Iu+MX4VWHRKBg5PCUK03ROnKgsC9pGvD1WmGTY00IVKEffBARP538b/EZmGYlOJ5+SqqjQ9gvfpxR+YRyStO+wo74kyCVdLCXptJkK6ZyfQk
 
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com;	b=f+us9nqA56ZDRPdqZAZpqdzIfNhhxToYr7PG2u5zdOyHFG0IJ4MFhxRTcEu4v9OW6mBCgsBe71bRQtfZCjrDrJiRZKb1rAzhA3CnHj5/u0o2m0L7EdgyyjQFsse7r6lB;
 
- Envelope-to: linda@xxxxxxxxxxxxxx
 
- List-id: <EnergyPlus_Support.yahoogroups.com>
 
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
 
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
 
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
 
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
 
- User-agent: eGroups-EW/0.82
 
Why setpoint-temperatures are not maintained in the zone?
The plant is into file : UTA
The control is:
Sizing:Zone,
    3P:3ESP,                 !- Zone Name
    16,                      !- Zone Cooling Design Supply Air Temperature {C}
    35,                      !- Zone Heating Design Supply Air Temperature {C}
    0.012,                   !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
    0.008,                   !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
    Flow/Person,             !- Outdoor Air Method
    0.00944,                 !- Outdoor Air Flow per Person {m3/s}
    ,                        !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Outdoor Air Flow per Zone {m3/s}
    ,                        !- Zone Heating Sizing Factor
    ,                        !- Zone Cooling Sizing Factor
    DesignDay,               !- Cooling Design Air Flow Method
    ,                        !- Cooling Design Air Flow Rate {m3/s}
    0.000762,                !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Cooling Minimum Air Flow {m3/s}
    ,                        !- Cooling Minimum Air Flow Fraction
    DesignDay,               !- Heating Design Air Flow Method
    ,                        !- Heating Design Air Flow Rate {m3/s}
    0.002032,                !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
    0.1415762,               !- Heating Maximum Air Flow {m3/s}
    0.3;                     !- Heating Maximum Air Flow Fraction
Sizing:System,
    air_loop,                !- AirLoop Name
    Sensible,                !- Type of Load to Size On
    autosize,                !- Design Outdoor Air Flow Rate {m3/s}
    1,                       !- Minimum System Air Flow Ratio
    35,                      !- Preheat Design Temperature {C}
    0.008,                   !- Preheat Design Humidity Ratio {kg-H2O/kg-Air}
    16,                      !- Precool Design Temperature {C}
    0.012,                   !- Precool Design Humidity Ratio {kg-H2O/kg-Air}
    16,                      !- Central Cooling Design Supply Air Temperature {C}
    35,                      !- Central Heating Design Supply Air Temperature {C}
    NonCoincident,           !- Sizing Option
    No,                      !- 100% Outdoor Air in Cooling
    No,                      !- 100% Outdoor Air in Heating
    0.0012,                  !- Central Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-Air}
    0.008,                   !- Central Heating Design Supply Air Humidity Ratio {kg-H2O/kg-Air}
    DesignDay,               !- Cooling Design Air Flow Method
    ,                        !- Cooling Design Air Flow Rate {m3/s}
    DesignDay,               !- Heating Design Air Flow Method
    ;                        !- Heating Design Air Flow Rate {m3/s}
Sizing:Plant,
    chiller_plantloop,       !- Plant or Condenser Loop Name
    Heating,                 !- Loop Type
    5,                       !- Design Loop Exit Temperature {C}
    7;                       !- Loop Design Temperature Difference {deltaC}
Sizing:Plant,
    boiler_plantloop,        !- Plant or Condenser Loop Name
    Heating,                 !- Loop Type
    80,                      !- Design Loop Exit Temperature {C}
    10;                      !- Loop Design Temperature Difference {deltaC}
ZoneControl:Thermostat,
    3P:3ESP Thermostat,      !- Name
    3P:3ESP,                 !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    Dual Setpoint - Zone 3P:3ESP;  !- Control 1 Name
ThermostatSetpoint:DualSetpoint,
    Dual Setpoint - Zone 3P:3ESP,  !- Name
    3P:3ESP Heating SP Sch,  !- Heating Setpoint Temperature Schedule Name  
    3P:3ESP Cooling SP Sch;  !- Cooling Setpoint Temperature Schedule
3P:3ESP Heating SP Sch,           May-Jun-Jul-Aug-Sep   Jan-Feb-Mar-Apr-Oct-Nov-Dec   h9-20  22°C
3P:3ESP Cooling SP Sch            May-Jun-Jul-Aug-Sep h9-20 24°C -- Jan-Feb-Mar-Apr-Oct-Nov-Dec  h9-20 22°C
SetpointManager:SingleZone:Heating,
    setpoint_heating,        !- Name
    Temperature,             !- Control Variable
    0,                       !- Minimum Supply Air Temperature {C}
    99,                      !- Maximum Supply Air Temperature {C}
    3P:3ESP,                 !- Control Zone Name
    Node PLF:PLFZ Zone,      !- Zone Node Name
    3P:3ESP Inlets,          !- Zone Inlet Node Name
    3esp_coil_heating_air_outlet_node;  !- Setpoint Node or NodeList Name
SetpointManager:SingleZone:Cooling,
    setpoint_cooling,        !- Name
    Temperature,             !- Control Variable
    0,                       !- Minimum Supply Air Temperature {C}
    40,                      !- Maximum Supply Air Temperature {C}
    3P:3ESP,                 !- Control Zone Name
    Node PLF:PLFZ Zone,      !- Zone Node Name
    3P:3ESP Inlets,          !- Zone Inlet Node Name
    3esp_coil_heating_air_outlet_node;  !- Setpoint Node or NodeList Name
SetpointManager:Scheduled,
    CW_supply_Temp_SP_schedule,  !- Name
    Temperature,             !- Control Variable
    CW_supply_Temp_Setpoint, !- Schedule Name
    CW_supply_outlet_node;   !- Setpoint Node or NodeList Name
Schedule:Compact,
    CW_supply_Temp_Setpoint, !- Name
    Temperature,             !- Schedule Type Limits Name
    through:12/31,           !- Field 1
    for:alldays,             !- Field 2
    until:24:00, 7;          !- Field 4
SetpointManager:Scheduled,
    HW_supply_Temp_SP_schedule,  !- Name
    Temperature,             !- Control Variable
    HW_supply_Temp_Setpoint, !- Schedule Name
    HW_supply_outlet_node;   !- Setpoint Node or NodeList Name
Schedule:Compact,
    HW_supply_Temp_Setpoint, !- Name
    Temperature,             !- Schedule Type Limits Name
    through:12/31,           !- Field 1
    for:alldays,             !- Field 2
    until:24:00, 70;         !- Field 4
thank,
valeria
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
    Individual Email | Traditional
<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)
<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/