[EnergyPlus_Support] Re: AFN width & height factor / detailed opening
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: AFN width & height factor / detailed opening
- From: "tobiasschulzeoooitu" <tobias.schulze@xxxxxxxxxxxxxx>
- Date: Wed, 08 Jun 2011 11:30:51 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Wed, 08 Jun 2011 05:31:05 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1307532664; bh=3fuY2hWQtcGKTb7LPzsbD6YwkaE2fNo56XasO2eg4bs=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=d76Lu2P1KyG9fa0dNNUUqQaTKNli82thaYq7wQcKyWrLLW9IEo05sW2WqKP9LUgzw60I3l7BWsBOSbFMFXvChLDs9c5DrQyp97KrjJXbKxB8DPY+6ZjNu/zlrGfbSLwi
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=D6c39P1UHrdI8HluZjy9sSpC1DVUxbcmBVuW7N10Xh87ceF5J2FptujqlGBDXSSFyTPIBnvC7B2X7GC1mvkrA7/yk1BGA5Ie9m54zJeK6b2MM/7hBkBrIB73WxWiWSdS;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <000001cc2526$e19b2d50$a4d187f0$@ucf.edu>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Dear Linxing,
the opening factor AFN:Surface is 1 as you told me to check. And the window geometry is also same - BUT the flow rates should be different because of the different opening geometry (as part of the window geo) due to the h&w factors. Lets say due to the h&w in factors in AFN:DetailedOpening I assumed that in 1) the opening is 0,1m wide and 1m high. And in 2) the opening is 1m wide and 0,1m high -> different opening geometry -> should result in different ACH.
3) and 4) are geometrically modelled and 3) is close 1)&2) and 4) is much less (less height = less ACH = correct)
BUT therefore I assume 2) to be wrongly calculated. Should be close to 4)
I compare the "AirflowNetwork Zone Infiltration Air Change Rate". No weather file necessary -> only DesignDay. In & Outdoor temp is fixed (20/24°C).
You can see that from the idf file containing all 4 scenarios. I will send you per mail (I hope it works).
What do you think?
Regards
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Lixing Gu <gu@...> wrote:
>
> Tobias:
>
> There are two issues. The first issue is window opening factor. If the
> opening factor for Cases 1 and 2 are 1.0, both windows should get the same
> flow rate due to the same geometry. Since the input files are not attached,
> you may check the opening factor by yourself first.
>
> The second issue is flow rate comparison. Since a two way flow is expected,
> what flow rate do you compare, incoming flow, outgoing flow or a sum?
>
> Please let me know what happens after check. You may also send your input
> files and provide weather date file name if the weather file is available in
> the web site. Then you need to specify which part of output file (rows and
> columns) make you think a program code fault.
>
> Thanks.
>
> Lixing
>
>
>
> -----Original Message-----
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of tobiasschulzeoooitu
> Sent: Monday, June 06, 2011 12:09 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] AFN width & height factor / detailed opening
>
> Hello,
>
> after some parametric analysis I realized, that for a single sided
> ventilation strategy, the volume flow is same for these two options:
> 1) width factor = 0,1 & height factor = 1
> 2) height factor = 0,1 & width factor = 1
>
> One can assume, that the volume flow in case 1) is higher because of the
> bidirectional opening model and higher density differences from top of the
> opening to the bottom of the opening as the opening height is bigger.
>
> Therefore I repeated the same cases, but changing the window geometry
> according the previously mentioned factors (leaving the factors as 1). Here
> the resulting volume flow for
> 3) opening width=0,1 & opening height=1
> is much higher than with a
> 4) opening height=0,1 & opening width=1
>
> This is as I assumed and flow for case 3)is very close to 1) & 2)
>
> Concluding, there may be is a program code fault with the opening factors
> when changing the height factor.
>
> Unfortunately the analytic solution for the cases as it is described in the
> engineering reference is very difficult to realize but I can send the 3 idf
> test files.
>
> Best Regards,
> Tobias
>
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to
> energyplus-support@...
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a
> high speed connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> Yahoo! Groups Links
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/