|
If it is for dual setpoint type 4 thermostat schedule, the heating and cooling temperature should not be the same. There should be a dead band in between although the band can be very small, say, 0.1°C. You have every thing in the plant (water heater, chiller etc.), air loop and the zone system, but there is no information on how they are used in the zone.
Is UTA a diagram of your system? The IDF itself would be more useful for debugging.
Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: valeba23@xxxxxxxxx Date: Wed, 8 Jun 2011 15:02:20 +0000 Subject: [EnergyPlus_Support] Re: zone temperature
thank,
but it is just my abbreviation for this message...into file is correct. --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@...> wrote: > > > I am not sure whether the thermostat schedules are correct. > > ZoneControl:Thermostat, > 3P:3ESP Thermostat, !- Name > 3P:3ESP, !- Zone or ZoneList Name > Zone Control Type Sched, !- Control Type Schedule Name > ThermostatSetpoint:DualSetpoint, !- Control 1 Object Type > Dual Setpoint - Zone 3P:3ESP; !- Control 1 Name > > ThermostatSetpoint:DualSetpoint, > Dual Setpoint - Zone 3P:3ESP, !- Name > 3P:3ESP Heating SP Sch, !- Heating Setpoint Temperature Schedule Name > 3P:3ESP Cooling SP Sch; !- Cooling Setpoint Temperature Schedule > > 3P:3ESP Heating SP Sch, May-Jun-Jul-Aug-Sep Jan-Feb-Mar-Apr-Oct-Nov-Dec h9-20 22°C > 3P:3ESP Cooling SP Sch May-Jun-Jul-Aug-Sep h9-20 24°C -- Jan-Feb-Mar-Apr-Oct-Nov-Dec h9-20 22°C > > I have not seen this format before. > > Dr. Li > > > > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx > From: valeba23@... > Date: Tue, 7 Jun 2011 15:23:52 +0000 > Subject: [EnergyPlus_Support] zone temperature > > > > > > > Why setpoint-temperatures are not maintained in the zone? > The plant is into file : UTA > The control is: > > Sizing:Zone, > 3P:3ESP, !- Zone Name > 16, !- Zone Cooling Design Supply Air Temperature {C} > 35, !- Zone Heating Design Supply Air Temperature {C} > 0.012, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air} > 0.008, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air} > Flow/Person, !- Outdoor Air Method > 0.00944, !- Outdoor Air Flow per Person {m3/s} > , !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} > , !- Outdoor Air Flow per Zone {m3/s} > , !- Zone Heating Sizing Factor > , !- Zone Cooling Sizing Factor > DesignDay, !- Cooling Design Air Flow Method > , !- Cooling Design Air Flow Rate {m3/s} > 0.000762, !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2} > , !- Cooling Minimum Air Flow {m3/s} > , !- Cooling Minimum Air Flow Fraction > DesignDay, !- Heating Design Air Flow Method > , !- Heating Design Air Flow Rate {m3/s} > 0.002032, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2} > 0.1415762, !- Heating Maximum Air Flow {m3/s} > 0.3; !- Heating Maximum Air Flow Fraction > > Sizing:System, > air_loop, !- AirLoop Name > Sensible, !- Type of Load to Size On > autosize, !- Design Outdoor Air Flow Rate {m3/s} > 1, !- Minimum System Air Flow Ratio > 35, !- Preheat Design Temperature {C} > 0.008, !- Preheat Design Humidity Ratio {kg-H2O/kg-Air} > 16, !- Precool Design Temperature {C} > 0.012, !- Precool Design Humidity Ratio {kg-H2O/kg-Air} > 16, !- Central Cooling Design Supply Air Temperature {C} > 35, !- Central Heating Design Supply Air Temperature {C} > NonCoincident, !- Sizing Option > No, !- 100% Outdoor Air in Cooling > No, !- 100% Outdoor Air in Heating > 0.0012, !- Central Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-Air} > 0.008, !- Central Heating Design Supply Air Humidity Ratio {kg-H2O/kg-Air} > DesignDay, !- Cooling Design Air Flow Method > , !- Cooling Design Air Flow Rate {m3/s} > DesignDay, !- Heating Design Air Flow Method > ; !- Heating Design Air Flow Rate {m3/s} > > Sizing:Plant, > chiller_plantloop, !- Plant or Condenser Loop Name > Heating, !- Loop Type > 5, !- Design Loop Exit Temperature {C} > 7; !- Loop Design Temperature Difference {deltaC} > > Sizing:Plant, > boiler_plantloop, !- Plant or Condenser Loop Name > Heating, !- Loop Type > 80, !- Design Loop Exit Temperature {C} > 10; !- Loop Design Temperature Difference {deltaC} > > ZoneControl:Thermostat, > 3P:3ESP Thermostat, !- Name > 3P:3ESP, !- Zone or ZoneList Name > Zone Control Type Sched, !- Control Type Schedule Name > ThermostatSetpoint:DualSetpoint, !- Control 1 Object Type > Dual Setpoint - Zone 3P:3ESP; !- Control 1 Name > > ThermostatSetpoint:DualSetpoint, > Dual Setpoint - Zone 3P:3ESP, !- Name > 3P:3ESP Heating SP Sch, !- Heating Setpoint Temperature Schedule Name > 3P:3ESP Cooling SP Sch; !- Cooling Setpoint Temperature Schedule > > 3P:3ESP Heating SP Sch, May-Jun-Jul-Aug-Sep Jan-Feb-Mar-Apr-Oct-Nov-Dec h9-20 22°C > 3P:3ESP Cooling SP Sch May-Jun-Jul-Aug-Sep h9-20 24°C -- Jan-Feb-Mar-Apr-Oct-Nov-Dec h9-20 22°C > > SetpointManager:SingleZone:Heating, > setpoint_heating, !- Name > Temperature, !- Control Variable > 0, !- Minimum Supply Air Temperature {C} > 99, !- Maximum Supply Air Temperature {C} > 3P:3ESP, !- Control Zone Name > Node PLF:PLFZ Zone, !- Zone Node Name > 3P:3ESP Inlets, !- Zone Inlet Node Name > 3esp_coil_heating_air_outlet_node; !- Setpoint Node or NodeList Name > > SetpointManager:SingleZone:Cooling, > setpoint_cooling, !- Name > Temperature, !- Control Variable > 0, !- Minimum Supply Air Temperature {C} > 40, !- Maximum Supply Air Temperature {C} > 3P:3ESP, !- Control Zone Name > Node PLF:PLFZ Zone, !- Zone Node Name > 3P:3ESP Inlets, !- Zone Inlet Node Name > 3esp_coil_heating_air_outlet_node; !- Setpoint Node or NodeList Name > > SetpointManager:Scheduled, > CW_supply_Temp_SP_schedule, !- Name > Temperature, !- Control Variable > CW_supply_Temp_Setpoint, !- Schedule Name > CW_supply_outlet_node; !- Setpoint Node or NodeList Name > > Schedule:Compact, > CW_supply_Temp_Setpoint, !- Name > Temperature, !- Schedule Type Limits Name > through:12/31, !- Field 1 > for:alldays, !- Field 2 > until:24:00, 7; !- Field 4 > > SetpointManager:Scheduled, > HW_supply_Temp_SP_schedule, !- Name > Temperature, !- Control Variable > HW_supply_Temp_Setpoint, !- Schedule Name > HW_supply_outlet_node; !- Setpoint Node or NodeList Name > > Schedule:Compact, > HW_supply_Temp_Setpoint, !- Name > Temperature, !- Schedule Type Limits Name > through:12/31, !- Field 1 > for:alldays, !- Field 2 > until:24:00, 70; !- Field 4 > > thank, > valeria > __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |