Did you look at the results of your simulation? Or just look at 1 number in the results file and then wonder what happened?

You need to analyze the results to see what is happening. Look at the zone temperatures and zone loads without using the EMS and then again when the EMS is used. Also look at the PTAC report variables to see how the operation has changed. Refer to the edd file to see if the EMS is working as you expect.

Output:Variable,*,Zone/Sys Air Temperature,hourly;
Output:Variable,*,Zone/Sys Air Temperature at Thermostat,hourly;
Output:Variable,*,Zone/Sys Sensible Load Predicted,hourly;
Output:Variable,*,Zone/Sys Sensible Load to Heating Setpoint Predicted,hourly;
Output:Variable,*,Zone/Sys Sensible Load to Cooling Setpoint Predicted,hourly;

Output:Variable,*,Packaged Terminal Air Conditioner Total Zone Heating Rate,hourly;
Output:Variable,*,Packaged Terminal Air Conditioner Total Zone Cooling Rate,hourly;
Output:Variable,*,Packaged Terminal Air Conditioner Sensible Zone Heating Rate,hourly;
Output:Variable,*,Packaged Terminal Air Conditioner Sensible Zone Cooling Rate,hourly;
Output:Variable,*,Packaged Terminal Air Conditioner Latent Zone Heating Rate,hourly;
Output:Variable,*,Packaged Terminal Air Conditioner Latent Zone Cooling Rate,hourly;
Output:Variable,*,Packaged Terminal Air Conditioner Electric Power,hourly;
Output:Variable,*,Packaged Terminal Air Conditioner Fan Part-Load Ratio,hourly;
Output:Variable,*,Packaged Terminal Air Conditioner Part-Load Ratio,hourly;

On 6/9/2011 6:16 PM, yusuf085225 wrote:
 

I try to model a six floors building with PTAC and EMS. when i use EMS for 1-5 floor, the total site energy is 1535GJ. then i try again EMS for 1-6 floor, the total site energy become 1593GJ. why the total site energy increase? when we use EMS, it should be more in energy efficiency, isn't it?

yusuf priyambodo


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___