[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] how can I change the HOT WATER PLANT HW SUPPLY PUMP power in a HVAC Template System VAV





Does this help?

  Pump:ConstantSpeed,
    autosize,                !- Rated Power Consumption {W}


On 6/16/2011 12:28 PM, Jim Dirkes wrote:
 

Dear Richard,

 

I’m missing something…. Where does “%NomPowerUse” come from?

 

To make sure we have the same understanding:

Pump power = Flow * DeltaP * ConversionFactor / Mechanical Efficiency / Motor Efficiency

 

You could also say:

Pump power = Flow * DeltaP * ConversionFactor / TotalEffic

 

Combining these efficiencies is essentially what you show:

PumpEffic =  TotalEffic / MotorEffic

 

Reformulating the 2nd equation above gives:

TotalEffic = Flow * DeltaP * ConversionFactor / Pump power

 

This basically matches your formula of:

TotalEffic =   FlowRate * PumpHead  /  NomPowerUse

 

Finally the question! EnergyPlus does not know the pump power use (when autosizing for example), so how can this equation be calculated without assuming something for pump efficiency?

I hope I’m not missing something obvious! (but I appear to be missing something!)

 

The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Richard Raustad
Sent: Thursday, June 16, 2011 11:31 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] how can I change the HOT WATER PLANT HW SUPPLY PUMP power in a HVAC Template System VAV

 

 

No. In the pump, motor efficiency is motor efficiency. Total eff is calculated as I showed. And in the fan, the fan efficiency input = (motor eff x fan eff) and motor eff is also an input. The fan and pump code was written by two different individuals long, long ago.

Your confusion may lie in the fact that the fan input field named Fan Efficiency might be better named Total Efficiency (power out divided by electrical power in). The phase "The fan efficiency is power..." in the description actually refers to the fan mechanical efficiency (power out divided by shaft power in).

Field: Fan Efficiency

The ratio of the power delivered to the fluid to the electrical input power. It is the product of the motor efficiency and the fan efficiency. The motor efficiency is the power delivered to the shaft divided by the electrical power input to the motor. The fan efficiency is power delivered to the fluid (air) divided by the shaft power. The power delivered to the fluid is the mass flow rate of the air multiplied by the pressure rise divided by the air density. Must be between 0 and 1.

On 6/16/2011 9:12 AM, Jim Dirkes wrote:

 

Well……

In order to calculate pump power, you must know flow, head, motor efficiency AND pump (mechanical) efficiency.  Since there is no input field for pump efficiency in E+, I looked into this a while back and the documentation indicated that the pump efficiency was a constant 78%.  Since you are indicating otherwise, I checked again and see that things appear to have changed!

So, is it the case that pumps now follow the E+ fan convention and use a combined (motor efficiency * pump mechanical efficiency) as the “Motor” efficiency input field?

p.s., I always thought that this was confusing, since it’s not a normal engineering convention and the field label clearly says “Motor efficiency”.  It’s workable, just confusing J.

 

The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Richard Raustad
Sent: Thursday, June 16, 2011 8:56 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] how can I change the HOT WATER PLANT HW SUPPLY PUMP power in a HVAC Template System VAV

 

 

The pump efficiency is not actually used in the calculation but it is calculated internally to provide warnings for the user. The Engineering Reference shows the pertinent calculations for the pump (search for "Variable Speed Pump" or "Constant Speed Pump").

The calculation for pump efficiency is:

TotalEffic =   PumpEquip(PumpNum)%NomVolFlowRate * PumpEquip(PumpNum)%NomPumpHead  / PumpEquip(PumpNum)%NomPowerUse

PumpEquip(PumpNum)%PumpEffic =  TotalEffic / PumpEquip(PumpNum)%MotorEffic


On 6/15/2011 7:31 PM, Jim Dirkes wrote:

 

.. and E+ always assumes pump efficiency to be a constant value (78% I think.)

 

The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jason Kirkpatrick
Sent: Wednesday, June 15, 2011 6:57 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] how can I change the HOT WATER PLANT HW SUPPLY PUMP power in a HVAC Template System VAV

 

 

Jose,

You can modify the pump power by changing the pump rated head in the HVACTemplate:Plant objects that you need to include to create the chilled water, hot water, and condenser water loops.

Pump Electric Power = Pump Volume Flow Rate  x  Pump Head /  Total Pump Efficiency

Refer to the EngineeringReference.pdf documentation that came with your install of energyplus for more detail.

Alternatively, once you have an expanded input data file that works, you could directly input the rated power consumption into the pump object and autosize the pump head.

In order to accomplish this you will need to rename the file that end with .expidf to a file with name .idf and then you can edit and run the expanded idf like any other input file.

Hope this is of help.

Jason

2011/6/14 José Ernesto Castillo Peralta <joercape@xxxxxxxxx>

 

Hi,

how can I change the power of the HOT WATER PLANT HW SUPPLY PUMP, CHILLED WATER PLANT CHW SUPPLY PUMP and CHILLED WATER PLANT CNDW SUPPLY PUMP in a HVAC Template System VAV

--

 

Jose Ernesto Castillo Peralta

 

 

 




-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
 
UCF - From Promise to Prominence: Celebrating 40 Years



-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
 
UCF - From Promise to Prominence: Celebrating 40 Years


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___