Are you reporting the zone relative humidity? If the zone moisture level is dropping, this would explain the difference. You need to keep the zone conditions constant for this to work.

On 6/17/2011 8:56 AM, yangxiaoshan@xxxxxxxx wrote:
 

Hi,
Thanks for your reply. I had set the infiltration rate to 0 or other values. If ACH is 0, there is no latent cooling load and total cooling load equals to total sensible cooling load. That makes sense. But once the ACH is not 0, the infiltration heat gain is always less than latent cooling load. I do not know what else items could be also included in the latent cooling load component.

Best,
Xiaoshan

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@...> wrote:
>
>
> Try changing the infiltration air change per hour to zero and to 2 to compare.
>
> There may be other compoent included in the total cooling load.
>
> Dr. Li
>
>
>
>
>
>
>
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> From: yangxiaoshan@...
> Date: Fri, 17 Jun 2011 06:37:59 +0800
> Subject: [EnergyPlus_Support] A question about Latent Cooling Load in E+
>
>
>
>
>
>
>
>
>
> Dear Colleagues,
>
>
> I got a question about latent cooling load in EnergyPlus. The simulation settings are: a single zone with constant cooling setpoint (26℃ through the day), no internal heat gain, 1 air changes per hour and "Idea Load Air System" automatically used for HVAC configuration. Theoratically, due to there is no internal heat gain in this case, the follow correlation should be valid: "Total cooling load - Total sensible cooling load = Latent cooling load = Infiltration latent heat gain". But the simulation results shown that the infiltration latent heat gain is always less than the latent cooling load (Total cooling load - Total sensible cooling load), 2% for this case (8-9% less was found in other simulation case). I cannot understand why the infiltration heat gain is not equal to the calculated latent cooling load. Really headache! Look forward to discussing with you, thanks very much.
>
> Best regards,
> Xiaoshan
>


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___