[EnergyPlus_Support] Re: Thermostat Float/Throttling Range



Generally, you are correct (not possible) although I have been able to mimic this type of control using EMS. I used negative process loads to cool a space which I turned on at the upper bound temp and off at the lower bound temp after checking that there is no heating on at the same time. Basically EMS allows little IF statements which are called during the normal simulation. It's a very nice part of e+.

You can manipulate a few object types including schedules, outputs, etc. Check out the EMS documentation.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "moe_wilensky" <moe_wilensky@...> wrote:
>
> From my initial look around this forum it would seem that on is unable to define a Thermostat Float/Throttling Range in Energy plus. Is this still the case?
> 
> For example , I want the cooling to kick on at 25, run until the temp is 23 and then turn off until the temp drifts back up to 25. is it possible to define the 2 degrees float on top of my 23 degree set point?
> 
> Thank you in advance for your time.
> 
> -Will
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/