|
The main issue is that you are probably only interested in PMV values during times when the building is occupied, or at least the when HVAC is on and the thermostats are not in setback/setup. A monthly frequency for Output:Variable should be the correct average but is for all the hours of the month regardless of operating intent. Output:Table:Monthly reports can be configured to produce averages for only those times when a second variable is non-zero and so can be used to obtain an average PMV for only times when the zone is occupied. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of amyquartette Hi everybody! __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |