Thanks, Richard.
The system node temperature values were displayed in Loong's csv. I did not know the significance of those high temperature values, as the chiller temperature values were normal. I increased the tower capacity by 100 times, (the values highlighted below) and the temperature values are now reduced from 1548°C to around 45°C. This may not be the correct way. There are still (18) warnings on his IDF error file. Dr. Li P.S. The change is highlighted below: CoolingTower:TwoSpeed, tower1, !- Name tower1 CndW Inlet, !- Water Inlet Node Name tower1 CndW Outlet, !- Water Outlet Node Name , !- Design Water Flow Rate {m3/s} autosize, !- Air Flow Rate at High Fan Speed {m3/s} autosize, !- Fan Power at High Fan Speed {W} , !- U-Factor Times Area Value at High Fan Speed {W/K} autosize, !- Air Flow Rate at Low Fan Speed {m3/s} autosize, !- Fan Power at Low Fan Speed {W} , !- U-Factor Times Area Value at Low Fan Speed {W/K} autosize, !- Air Flow Rate in Free Convection Regime {m3/s} , !- U-Factor Times Area Value at Free Convection Air Flow Rate {W/K} NominalCapacity, !- Performance Input Method 2000000, !- High Speed Nominal Capacity {W} 1000000, !- Low Speed Nominal Capacity {W} 200000, !- Free Convection Capacity {W} , !- Basin Heater Capacity {W/K} , !- Basin Heater Setpoint Temperature {C} , !- Basin Heater Operating Schedule Name , !- Evaporation Loss Mode 0.2, !- Evaporation Loss Factor {percent/K} 0.008, !- Drift Loss Percent {percent} , !- Blowdown Calculation Mode 3, !- Blowdown Concentration Ratio , !- Blowdown Makeup Water Usage Schedule Name , !- Supply Water Storage Tank Name tower1 Cooling Tower Outdoor Air Inlet Node, !- Outdoor Air Inlet Node Name , !- Number of Cells , !- Cell Control , !- Cell Minimum Water Flow Rate Fraction , !- Cell Maximum Water Flow Rate Fraction 1; !- Sizing Factor To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: RRaustad@xxxxxxxxxxxx Date: Wed, 6 Jul 2011 13:32:44 -0400 Subject: Re: å??å¤?ï¼? [EnergyPlus_Support] PsyPsatFnTemp+PsyTsatFnHPb
The psyc routines do have limits on inputs. The PsyPsatFnTemp
routine returns saturation pressure (Psat) as a function of
temperature (Temp). This routine is usually used to calculate RH or
wet-bulb temperature. But this is really beside the point. The air
temperature input to this routine is 1898.61 C. This is way out of
bounds. I would report the air node temperatures in your simulation
and see if you can find a node with this high of a temperature which
may then help you determine what is happening in your simulation.
Output:Variable,*,System Node Temp,Hourly; On 7/6/2011 1:13 PM, YuanLu Li wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |