Hi, Pablo
Your IDF does not produce a valid DXF file, so there may be problem in the building model.
The Zone:Unitary is not required, as you are not using any components. But the termostat is used and is therefore may not be available for the System:Unitary object. The outdoor air mixer is also double declared. Therefore the template macro cannot be correctly expanded.
If you are in a hurry to get the solution, you should send this to the EPlus help desk.
The group of templates to use is in the I/O manual.
=============================
HVACTemplate:Zone:Unitary,
ZONA 5 NIVEL 3, !- Zone Name
AA_1 Z5 N3, !- Template Unitary System Name
T ZONA 5 N3, !- Template Thermostat Name
autosize, !- Supply Air Maximum Flow Rate {m3/s}
0, !- Zone Heating Sizing Factor
0, !- Zone Cooling Sizing Factor
Flow/Person, !- Outdoor Air Method
, !- Outdoor Air Flow Rate per Person {m3/s}
, !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
, !- Outdoor Air Flow Rate per Zone {m3/s}
, !- Supply Plenum Name
, !- Return Plenum Name
None, !- Baseboard Heating Type
, !- Baseboard Heating Availability Schedule Name
autosize; !- Baseboard Heating Capacity {W}
-----------------
Nothing is used in the above object.
=================
HVACTemplate:System:Unitary,
AA_1 Z5 N3, !- Name
AA_HVAC Z5 N3, !- System Availability Schedule Name
ZONA 5 NIVEL 3, !- Control Zone or Thermostat Location Name
0.57, !- Supply Fan Maximum Flow Rate {m3/s}
Cycling, !- Supply Fan Operating Mode Schedule Name
0.7, !- Supply Fan Total Efficiency
600, !- Supply Fan Delta Pressure {Pa}
0.9, !- Supply Fan Motor Efficiency
1, !- Supply Fan Motor in Air Stream Fraction
SingleSpeedDX, !- Cooling Coil Type
, !- Cooling Coil Availability Schedule Name
9672, !- Cooling Coil Capacity {W}
autosize, !- Cooling Coil Rated Sensible Heat Ratio
2.64, !- Cooling Coil Rated COP
Gas, !- Heating Coil Type
, !- Heating Coil Availability Schedule Name
autosize, !- Heating Coil Capacity {W}
0.8, !- Gas Heating Coil Efficiency
, !- Gas Heating Coil Parasitic Electric Load {W}
autosize, !- Maximum Outdoor Air Flow Rate {m3/s}
autosize, !- Minimum Outdoor Air Flow Rate {m3/s}
, !- Minimum Outdoor Air Schedule Name
NoEconomizer, !- Economizer Type
NoLockout, !- Economizer Lockout
, !- Economizer Upper Temperature Limit {C}
, !- Economizer Lower Temperature Limit {C}
, !- Economizer Upper Enthalpy Limit {J/kg}
, !- Supply Plenum Name
, !- Return Plenum Name
BlowThrough, !- Supply Fan Placement
StayOff, !- Night Cycle Control
, !- Night Cycle Control Zone Name
None, !- Heat Recovery Type
I have a problem with a idf, where idf pretend I get the errors shown in the attachment.
I've created my air conditioning systems HVAC objects: Template: Zone: Unitary and VAC: Template: System: Unitary, then objects appear in the error file must be created themselves. ** Severe ** Node Connection Error, Node="AA_1 Z2 N2 AIR LOOP INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=AA_1 Z2 N2 MAIN BRANCH
** Severe ** Node Connection Error, Node="AA_1 Z1 N3 AIR LOOP INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=AA_1 Z1 N3 MAIN BRANCH
** Severe ** Node Connection Error, Node="AA_1 Z3 N3 AIR LOOP INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=AA_1 Z3 N3 MAIN BRANCH
** Severe ** Node Connection Error, Node="AA_2 Z3 N3 AIR LOOP INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=AA_2 Z3 N3 MAIN BRANCH
** Severe ** Node Connection Error, Node="AA_3 Z3 N3 AIR LOOP INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=AA_3 Z3 N3 MAIN BRANCH
** Severe ** Node Connection Error, Node="AA_4 Z3 N3 AIR LOOP INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=AA_4 Z3 N3 MAIN BRANCH
** Severe ** Node Connection Error, Node="AA_1 Z4 N3 AIR LOOP INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=AA_1 Z4 N3 MAIN BRANCH
** Severe ** Node Connection Error, Node="AA_1 Z5 N3 AIR LOOP INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=AA_1 Z5 N3 MAIN BRANCH
** Severe ** Node Connection Error, Node="AA_1 Z2 N1 AIR LOOP INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=AA_1 Z2 N1 MAIN BRANCH
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=20774/stime=1310087508>
Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmNGpjaHViBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzMTAwODc1MDg->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkaHI2Y3A2BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzEwMDg3NTA4>Visit Your Group | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe
__,_._,___