RE: [EnergyPlus_Support] opening windows
You can try 1 m/s as the comfortable air velocity. Window unit has a higher air discharge velocity than this.
Multiply this by the window area to get the air flow rate. Use EPlus to calculate the ACH rate to compare. Use a Window open schedule to turn on the infiltration object at night.
I think the infiltration object will close the window for you when the external wind velocity is high.
Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: robin.cris@xxxxxxxxx
Date: Fri, 8 Jul 2011 11:24:52 +0000
Subject: [EnergyPlus_Support] opening windows
Hello All
What is the easiest way to open windows?
Lets say that I got a rectangle one zone model with 1 window on each wall.
I want to open 2 windows from 19:00-7:00 at night.