[EnergyPlus_Support] Problem with removing reheat coils in VAV



Hi!

I'm trying to simulate an existing HVAC system which is similar to a VAV, only with heating, without cooling coil or reheat coils. I'm using the HVAC Template VAV Packaged.
The rooms' temperatures stay above 20ºC, like I configured in the Thermostat, until I remove the reheat coils. When I do that the temperature drops under 20ºC and only reaches it if there are internal loads.

I have almost everything in autosize, except the maximum flow of the input air (but autosize never reaches it, so I think the problem is not from there).

To see my problem just open this example file that comes with EnergyPlus: HVACTemplate-5ZonePackagedVAV.idf. Then run a simulation and consult the evolution of Zone Air Temperature for any of the conditioned zones and see that it stays inside the temperatures of the Thermostat. After that go to the file, remove the reheat coils of every zone (and deactivate the system cooling coil), run the simulation again and compare the temperatures. You'll see that now the temperatures stay under the Thermostat limit and only reach it when the internal loads harm the room enough.

I'm looking in the expidf file for days and I still don't know what is wrong with it. Since I really have to remove the reheat coils, what can I do to correct this problem?

Thanks in advance!



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/