Add these report variables to your file. You should see them in the rdd file after a simulation. The PLR is the cycling that occurs when a cycling fan system operates to meet a load. The RTF is slightly greater than PLR and includes losses due to cycling (i.e., the system has to run a little longer to overcome cycling losses). the PLR is used when calculating loads and how long the system needs to operate to meet the load. The RTF is used to calculate power use. Output:Variable,*,Packaged Terminal Air Conditioner Part-Load Ratio,Hourly; Output:Variable,*,DX Cooling Coil Runtime Fraction,timestep; On 7/11/2011 1:26 PM, Aditya Ravi wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.