|
I think you are not isolating the problems and focus on what you need.
My comments are in Red below. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: n_junk@xxxxxxxxxxxxxx Date: Mon, 18 Jul 2011 17:21:36 -0700 Subject: [EnergyPlus_Support] Re: Problem with removing reheat coils in VAV Hi, With the things that you said in mind, I tried some solutions and I solved a part of the problem, removing the autosize for the Heating Design Air Flow Rate and inserting a constant value. The problem was caused by the high value of internal lighting. The building does not require heating in Winter. Hence the VAV template does not work well with the reheat and the OA adjustment by economizer. If your real building do not have the similar situation, this need not be investigate further. When I changed the dampling minimum to 0.2 in space5, the zone5 damper moved to below 0.3, while all the other demper which was set to 0.3 remained at 0.3. This means that space5 is controlling the system. As the thermostat is now in cooling mode, 24°C is the controlled value. All the other zones simply left the damper at the minimum condition. The solution may be to used another minimum control mode for the damper, so that the damper can be closed down further. That forced the heating of the zones. Of course there are still some strange values but I know that it just needs some tweaking. Tweaking on the current IDF may not be what you need for your final design, which may have a different charcteristic, and the problem may not arise.. The problem now is that I don't want a heating coil of gas, like the current one that is on the system, I need to simulate a heating coil of (hot) water, and when I change the heating coil from gas to water the zones' heating rolls back to where they were, malfunctioning again. I then installed an extra electric heating coil after the water heating coil and then the heating worked with no problems. I think that with this I prove that the problem is coming from the water or plant loop. Gas heater and water coil heater do not have the same characteristic. Therefore, you are back to have more problems. But I don't know what is specifically going wrong. If you analyze the results spreadsheet you will see that the water enters the heating coil and leaves it without changing its temperature. It's like the heating coil is not functioning at all. Because the building is not in the heating mode, due to high internal load. Therefore, the heating coil is not used. The cooling is on in Winter, when I looked at the spread sheed using the template IDF I send you.(without reheat and economizer by entering non and noEconomizer in the zone and system object..). More strange than that is that the program is autosizing it anyway. I can't understand how something that doesn't work has a calculated heating capacity. I am not sure. May be the EPlus is also looking the building requirement without the internal load. I will try to attach the new file. Note that it will go with the electric heating coil, with the schedule "always off". To activate it just change the schedule. I have not looked at the new IDF yet. For a system to work, you should not force the system off manually with a schedule. That was the reason why I asked you to watch the damper position by turning off the peak lighting in the schedule at different times of the day for the WinterDesignDay. Sorry in advance if any of the values are misleading or the names are not very simple or if they are badly defined. It's just very difficult to me to mantain all this variables in control with so much changes and I'm really tired from being days and nights trying to solve this. My biggest questions are, at this moment, is there a way to change the priority of the heating coils? Yes, in the zone equipment section. But that will make no difference, if you are heating in Winter. And second, what I'm doing wrong in the boiler, hot water loop or heating coil? Remember that I'm a rookie in EPlus, so check first for a basic error or common mistake. Do not try to modify the expIDF. Fill in the details correctly in the template or find another tamplate to use. or use District heating for the boiler in the plant. I am not sure whether the district heating can be connected directly to the water heating coil. If your final design has a fan coil in the zone, the configuration will be all different. That was the reason why I ask you whether your 5 AHU is for a 5 zone building or a 5 storey building with many zones per AHU.
Once again many thanks to you. Without your help in this last days I couldn't go any further! --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "n_junk" <n_junk@...> wrote: > > > You gave me a lot to think, many thanks! I got some ideas that might work. I will keep you posted with the results. > > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@> wrote: > > > > > > Hi, Lixeira I assume that the IDF you used was HVACTemplate-5ZonePackagedVAV.idf > > The following was extract from the expIDF without your editing.ã?? > > =============================ã?? > > SetpointManager:Scheduled, DXVAV Sys 1 Cooling Supply Air Temp Manager, !- Name Temperature, ! Control Variable HVACTemplate-Always 12.8, ! Schedule Name DXVAV Sys 1 Supply Fan Outlet; ! Setpoint Node or NodeList Name > > > > The template program has generated a schedule for you and used the temprature 12.8 C for the cool air output of the system.Because this is low compared with the zone thermostat setting, the reheat coil is uded to heat the zone to the required temperature. Find this compact schedule in your expIDF and change it to 22 or 23°C. and rename it to IDF with a diffeent name. The reheat coil should stop working. You can also change the reheat coil avilability schedule to always OFF. Then the zone will be cold, unless you turn on more lights. This is another way to test the program, with your own added heating. If the reheat power is 1000 watt, add 1100 watt to your lighting would turn off the reheat of that zone.==========SetpointManager:MixedAir, DXVAV Sys 1 Cooling Coil Air Temp Manager, !- Name Temperature, ! Control Variable DXVAV Sys 1 Supply Fan Outlet, ! Reference Setpoint Node Name DXVAV Sys 1 Heating Coil Outlet, ! Fan Inlet Node Name DXVAV Sys 1 Supply Fan Outlet, ! Fan Outlet Node Name DXVAV Sys 1 Mixed Air Nodes; ! Setpoint Node or NodeList Name > > > > This manager defines the fan locatin and the mixed air node to be controlled to the temperature in the schedule which was set to 12.8.=================! NOTE: Heating supply air setpoint is placed on Supply Path Inlet node to allow separate heating and cooling setpoints. > > ! SetpointManager:MixedAir <system name> Heating Coil Air Temp Manager adjusts this setpoint for fan heat and places it on the Heating Coil Outlet > > > > This note explains why you have two MixedAir managers. Draw a diagram to see where these nodes are in the air loop system. SetpointManager:Scheduled, > > DXVAV Sys 1 Heating Supply Air Temp Manager, !- Name Temperature, ! Control Variable HVACTemplate-Always 10, ! Schedule Name DXVAV Sys 1 Supply Path Inlet; ! Setpoint Node or NodeList Name > > > > SetpointManager:MixedAir, DXVAV Sys 1 Heating Coil Air Temp Manager, !- Name Temperature, ! Control Variable DXVAV Sys 1 Supply Path Inlet, ! Reference Setpoint Node Name DXVAV Sys 1 Heating Coil Outlet, ! Fan Inlet Node Name DXVAV Sys 1 Supply Fan Outlet, ! Fan Outlet Node Name DXVAV Sys 1 Heating Coil Outlet; ! Setpoint Node or NodeList Name > > > > Because this is set to 10°C, the reheat heater is used to heat the zone to 20°C. So change this to 19°C may stop the reheat.The temperature are normally set this way so that indivitual zones can have its own make up heating source. ========================Controller:OutdoorAir, DXVAV Sys 1 OA Controller, ! Name DXVAV Sys 1 Relief Air Outlet, ! Relief Air Outlet Node DXVAV Sys 1 Air Loop Inlet, ! Return Air Node Name DXVAV Sys 1 Mixed Air Outlet, ! Sensor Node Name DXVAV Sys 1 Outside Air Inlet, ! Actuated Node autosize, ! minimum outside air flow rate {m3/s} autosize, ! maximum outside air flow rate {m3/s} DifferentialDryBulb, ! Economizer Control Type ModulateFlow, ! Economizer Control Action Type 19, ! Fixed Dry Bulb Temperature Limit {C} , ! Fixed Enthalpy Limit {J/kg} , ! Fixed Dew Point Temperature Limit (C) , ! Electronic Enthalpy Limit Curve Name 4, ! Dry Bulb Temperature Lower Limit {C} NoLockout, ! Lockout Type ProportionalMinimum, ! Minimum Limit Type Min OA Sched, ! Minimum Outdoor Air Schedule Name , ! Minimum Fraction of Outdoor Air Schedule Name , ! Maximum Fraction of Outdoor Air Schedule Name ; ! Mechanical Ventilation Controller Name This controller has economizer action. When the outdoor air is between 3 to 19°C, the outdoor air can be used for air temperature adjustment.====================== > > > > Hope this will help to explain how the setpoint managers work in your IDF. Dr. Li > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx > > From: n_junk@ > > Date: Sun, 17 Jul 2011 01:23:15 +0000 > > Subject: [EnergyPlus_Support] Re: Problem with removing reheat coils in VAV > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Hi Dr. Li, > > > > > > > > Many thanks for your assistance! > > > > I'm trying to analyze what you've said and see what I can change in my file. > > > > > > > > Since it's my first simulation in energyplus, I'm still trying to learn the basics. > > > > One thing that it's very odd to me and I can't understand at all it's the behavior of the heating coils of the system. I really don't know what is controlling them, in the program. Everytime I deactivate (not remove, just shut them off) the reheat coils in the zones, the heating coil of the main system seems to just turn off, even if I put setpoints in the heating coil outlet temperature or rise the design temperature. It's like the program quits to care about controlling the setpoint temperatures I inserted everytime I shut off the reheat coils. > > > > > > > > I was expecting something far more easy and simple, that when I removed the reheat coils the program would 'think': «ok, since I can't rely anymore on the reheat coils, I need to heat more the air in the system's heating coil, so I will rise the heating coil's capacity». If I'm just shutting off the reheat coils, and not removing anything, and even rising the "heating coil design setpoint" in the HVACTemplate:System:PackagedVAV, what is going so wrong that shuts off or undersizes the heating coil's capacity, makes the setpoint temperatures not being met and doesn't heat the zones as expected? > > > > > > > > Please note again that I'm still learning the basics of EnergyPlus and I'm using the HVACTemplates as a starting point, and then editing the expidf file, because it would be impossible to me to design all the air, system and plant loops, with my current knowledge, in time to deliver my thesis. > > > > > > > > Once again, thanks in advance! > > > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@> wrote: > > > > > > > > > > > > > > > > > > > > Hi, Lixeira I think you are trying to replace the usual air loop with one master zone thermostat control with one which uses the set point manager to control the air loop temperature and variable damper at the zone without reheat coil. In this way all thermostat are available in each zone. Because you are using setpoint manager for the air loop, the temperature should not be a range, but one temperature slightly below the wanted zone temperature. This difference is normally compensated by reheat. The heating should also be slightly lower. The type 4 dead band should also be maintained at the zone, with modified schedules. When the OA is cool in Summer, your system is turning on the heater to keep the temperature at the zone thermostat setting. > > > > > There is no severe error. Just need some tuning on the available schedules and set point values or managers. AirTerminal:SingleDuct:VAV:NoReheat, should not be running at constant mode. I do not know how to change this yet. What I did of my own project was to use the one with reheat and disable the coil, not removing it, so that the damper will still have control of the air flow. Because the zone demand loads are not the same and dampers are not controlled, therefore the temperatures are all different. Dr. Li > > > > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx > > > > > From: n_junk@ > > > > > Date: Sat, 16 Jul 2011 09:39:20 -0700 > > > > > Subject: [EnergyPlus_Support] Re: Problem with removing reheat coils in VAV > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Hi Jean, > > > > > > > > > > I'm sending the file that I'm testing as an e-mail attachment. I hope that the attachment will be send and received without errors. > > > > > Note that the "plenum" temperatures are not controlled, but all the "spaces" temperatures should be controlled (always above 20ºC). > > > > > Could the problem be in the VAV terminal damper position? > > > > > > > > > > Thanks in advance! > > > > > > > >
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |