[EnergyPlus_Support] Re: Missing Field?



I changed the definition to include an additional AND UNDOCUMENTED FIELD to include the extra "AHU Reheater Outlet;" and now it seems to be running. Please check this, eplus support.




--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean marais" <jeannieboef@...> wrote:
>
> I'm trying to insert a electric heating coil for reheat and get
> 
>  ** Severe  ** Coil:Heating:Electric "AHU REHEATER"
>    **   ~~~   ** ... Missing control node for heating coil.
>    **   ~~~   ** ... enter a control node name in the coil temperature setpoint node field for this heating coil.
>    **   ~~~   ** ... use a Set Point Manager to establish a setpoint at the coil temperature setpoint node.
> 
> There is no field for "control node name" in "Coil:Heating:Electric" and also no controller to be used with it.
> 
> My definition is
> 
>   Coil:Heating:Electric,
>     AHU Reheater,            !- Name
>     2,                       !- Availability Schedule Name
>     0.99,                    !- Efficiency
>     600000,                  !- Nominal Capacity {W}
>     DOAS Supply Fan Outlet,  !- Air Inlet Node Name
>     AHU Reheater Outlet,     !- Air Outlet Node Name
>     AHU Reheater Outlet;     
> 
> SetpointManager:Scheduled,
>     Supply Air Temp Manager 1, !- Name
>     Temperature, !- Control Variable
>     AHU Supply Air Temp Sch, !- Schedule Name
>     SetpointNodes; !- Setpoint Node or NodeList Name
>     
> NodeList,
>   SetpointNodes,                                     !- Name
>   AHU Reheater Outlet;                                    !- Node ID    
> 
> Schedule:Compact,
> AHU Supply Air Temp Sch,
> Any Number,
> Through: 12/31,
> For: AllDays,
> Until: 24:00, 18;
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/