It's telling you that the design parameters do not conform with psychrometrics. Usually, design values for water-side and air-side are 5.5C and 11.1C, respectively. Your air-side delta T does not provide this value. Now you can operate at a supply air temperature of 18C if you like, but you should "size" the coil differently. As the message states, I would change the sizing information accordingly. I have tried this and it still leads to the same error, hopefully this won't happen to you. So I am not exactly sure if the error will disappear without some iteration. If you do want to size your coil for an exiting air temperature of 18C at this air flow, entering air condition, and water temp/flow rate, then you will have to manually size the coil to get there. The amount of reheat you use will depend on the supply air temperature (your 18C) and flow rate vs the zone loads. You can also reset the supply air temperature based on outdoor temperature (SetpointManager:OutdoorAirReset) to help reduce the amount of reheat. On 7/29/2011 10:38 AM, Jean marais wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |