[EnergyPlus_Support] Re: AFN - Nat Vent Too much during cold / warm days



Hi,

1. Since you select "constant" on the surface level, there is always air flow on your outer openings (as much as your venting availability schedules permits). If you want to consider temperature modulation of air flow, you should set vent. control mode on surface level as temperature. Secondly, you may work on crack factor on this level.

2. You should work on some parameters on DetailedOpening which are related to when the openings are closed. 

3. Also consider your cracks' conditons on surface level.

Hope to help you, 

Zeynep

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean marais" <jeannieboef@...> wrote:
>
> hi All, I'm seeing large air change rates (10-20 ACH) when the outdoor temp is at 7 degC and indoor temp is at 21 degC. The "Zone" level control is set for dT of 5 degC and the "surface" level control is set for "constant". See below...please advise.
> 
>   AirflowNetwork:MultiZone:Zone,
>     118129,                  !- Zone Name
>     Temperature,             !- Ventilation Control Mode
>     20001,                   !- Ventilation Control Zone Temperature Setpoint Schedule Name
>     0,                       !- Minimum Venting Open Factor {dimensionless}
>     0,                        !- Indoor and Outdoor Temperature Difference Lower Limit For Maximum Venting Open Factor {deltaC}
>     5,                       !- Indoor and Outdoor Temperature Difference Upper Limit for Minimun Venting Open Factor {deltaC}
>     ,                        !- Indoor and Outdoor Enthalpy Difference Lower Limit For Maximum Venting Open Factor {deltaJ/kg}
>     ,                        !- Indoor and Outdoor Enthalpy Difference Upper Limit for Minimun Venting Open Factor {deltaJ/kg}
>     12345;                   !- Venting Availability Schedule Name
> 
> AirflowNetwork:MultiZone:Surface,
>     P_118129_1_0_0_0_0_0_Win,!- Surface Name
>     P_118129_1_0_0_0_0_0_Win,!- Leakage Component Name
>     P_118129_1_0_0_0_0_0_Win,!- External Node Name
>     1,                       !- Window/Door Opening Factor, or Crack Factor {dimensionless}
>     Constant,                !- Ventilation Control Mode
>     20001,                   !- Ventilation Control Zone Temperature Setpoint Schedule Name
>     .01,                     !- Minimum Venting Open Factor {dimensionless}
>     0,                       !- Indoor and Outdoor Temperature Difference Lower Limit For Maximum Venting Open Factor {deltaC}
>     15,                      !- Indoor and Outdoor Temperature Difference Upper Limit for Minimun Venting Open Factor {deltaC}
>     ,                        !- Indoor and Outdoor Enthalpy Difference Lower Limit For Maximum Venting Open Factor {deltaJ/kg}
>     ,                        !- Indoor and Outdoor Enthalpy Difference Upper Limit for Minimun Venting Open Factor {deltaJ/kg}
>     2;                       !- Venting Availability Schedule Name
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/