This probably relates to your problem. You tell the program to chose the inlet air humrat, but then specify the outlet air humrat. autosize, !- Design Inlet Air Humidity Ratio {kg-H2O/kg-air} 0.0010, !- Design Outlet Air Humidity Ratio Entering is 0.01178 ,0.0050 does not work I would run the program for the sizing period and report the outdoor T and W to see how these values change. That warning looks like one that should provide more information. Alternately you could specify both or autosize both. On 8/3/2011 8:52 AM, Jean marais wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.