Ok,
i have integrated an EMS code to avoid the problem. But i
was thinking that it was possible to change parameters to
solve it.
Thanks all.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx,
Richard Raustad <RRaustad@...> wrote:
>
> You already have the answer from the previous email.
>
> Here, it has first run a system timestep of 10
minutes (from 8:10 to
> 8:20), then later decided it should be shorter and
repeated a system
> timestep that starts at 8:10 (from 8:10 to 8:13).
Because of this and
> other iteration/timing issues, you will have a hard
time counting up
> time entirely on your own.
>
> The simulation ran at 8:10-8:20 and found that it had
to shorten the
> system time step. So it ran that time again, but this
time from 8:10 -
> 8:13.333, and then 8:13.333 - 8:16.667, and then
8:16.667 - 8:20. So the
> time 8:10-8:20 was repeated, this is where your error
is. You have to
> account for that in your EMS code.
>
> This example should give you an idea of what you need
to do.
>
> IF(SystemTimeStep < LastSysTStep)THEN
> SET count = count - LastSysTStep
> END IF
> SET count = count + SystemTimeStep
> SET LastSysTStep = SystemTimeStep
>
> On 8/3/2011 5:34 AM, dgerome06 wrote:
> >
> > I am already using built-in variable
SystemTimeStep. My program is
> > simple, just count the time spent during the
simulation.
> >
> > Program :
> > SET count = count + SystemTimeStep
> >
> > The program is called
"AfterPredictorAfterHVACManagers"
> >
> > The outputvariable "count" is type "summed" and
frequency
> > "systemtimestep".
> >
> > My timestep is 10min that is to say 0.167 hours.
> > The right column of the next array is what i
expect to have and the
> > left column is what i have in the spreadsheet.
> >
> > 33 33
> > 33,16666667 33,16666667
> > 66,91666667 33,33333333
> > 67,58333333 33,5
> > 68,25 33,66666667
> > 68,91666667 33,83333333
> > 69,58333333 34
> > 70,25 34,16666667
> > 106,3333333 34,33333333
> > 107,3333333 34,5
> > 72,25 34,66666667
> > 36,33333333 34,83333333
> > 36,5 35
> >
> > This problem doesn't happen with a timestep of
2min.
> > I want to work with timestep=10 min so i need to
find a solution.
> >
> > I can send the edd file maybe it will be easier
to understand.
> >
> >
>
> --