Thank you all for the help. After Lixing's reply, EMS is exactly what I was thinking. Thanks for the code, Sam, that saves me precious time (I'll have to discuss the royalties with my boss then I guess ;). Thankfully, I've got a bit of practice with EMS under my belt already.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "samuel.brunswick" <samuel.brunswick@...> wrote:
>
> Hi Jean,
>
> You can modulate the opening factor using any variable by writing your own EMS control code. I've done this before (modulating based on m3/s) and have pasted an example below if you want to copy it. I'll expect royalties.
>
> However, high ACH shouldn't be a problem unless it affects occupant comfort in some way. Two ways it can do this are high air speeds (in excess of ~1m/s) or letting in too much cold air and cooling the space.
>
> If you are letting in too much cold air, you might want to refine your zone dT modulation parameters. Yours look reasonable however, unless maybe your windows are large compared to your zone.
>
> If your air speeds are too high [you can get a rough approximation of the jet speed at the window by dividing the volumetric flow rate (m3/s) by the opening area of the window (m2)] then you might consider adding an EMS controller like I've pasted below. This example modulates two windows separately.
>
> Hope this helps.
>
> Sam
>
> !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:SENSOR ===========
>
> EnergyManagementSystem:Sensor,
> FlowIn288, !- Name
> Win_288, !- Output:Variable or Output:Meter Index Key Name
> AirflowNetwork Volume Flow Rate from Node 2 to 1; !- Output:Variable or Output:Meter Name
>
> EnergyManagementSystem:Sensor,
> FlowOut288, !- Name
> Win_288, !- Output:Variable or Output:Meter Index Key Name
> AirflowNetwork Volume Flow Rate from Node 1 to 2; !- Output:Variable or Output:Meter Name
>
> EnergyManagementSystem:Sensor,
> FlowIn289, !- Name
> Win_289, !- Output:Variable or Output:Meter Index Key Name
> AirflowNetwork Volume Flow Rate from Node 2 to 1; !- Output:Variable or Output:Meter Name
>
> EnergyManagementSystem:Sensor,
> FlowOut289, !- Name
> Win_289, !- Output:Variable or Output:Meter Index Key Name
> AirflowNetwork Volume Flow Rate from Node 1 to 2; !- Output:Variable or Output:Meter Name
>
>
> !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:ACTUATOR ===========
>
> EnergyManagementSystem:Actuator,
> OpenFactor288, !- Name
> Win_288, !- Actuated Component Unique Name
> AirFlow Network Window/Door Opening, !- Actuated Component Type
> Venting Opening Factor; !- Actuated Component Control Type
>
> EnergyManagementSystem:Actuator,
> OpenFactor289, !- Name
> Win_289, !- Actuated Component Unique Name
> AirFlow Network Window/Door Opening, !- Actuated Component Type
> Venting Opening Factor; !- Actuated Component Control Type
>
>
> !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAMCALLINGMANAGER ===========
>
> EnergyManagementSystem:ProgramCallingManager,
> ProgramCallingManager1, !- Name
> BeginTimestepBeforePredictor, !- EnergyPlus Model Calling Point
> FlowRateLimitProgram; !- Program Name 1
>
>
> !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAM ===========
>
>
> EnergyManagementSystem:Program,
> FlowRateLimitProgram, !- Name
> set FlowrateIn288=FlowIn288, !- Program Line 1
> set FlowrateOut288=FlowOut288, !- Program Line 2
> If (FlowrateIn288 > 15.0),!- A4
> Set OpenFactor288 = 0,!- A5
> ElseIf (FlowrateIn288 > 3.0),!- A4
> Set OpenFactor288 = 0.7,!- A5
> ElseIf (FlowrateIn288 > 2.5) && (FlowrateIn288<= 3.0), !- A6
> Set OpenFactor288 = 0.75, !- A7
> ElseIf (FlowrateIn288 > 2.0) && (FlowrateIn288<= 2.5), !- A8
> Set OpenFactor288 = 0.8,!- A9
> ElseIf (FlowrateOut288 > 3.0), !- A10
> Set OpenFactor288 = 0.7,!- A11
> ElseIf (FlowrateOut288 > 2.5) && (FlowrateOut288<= 3.0), !- A12
> Set OpenFactor288 = 0.75, !- A13
> ElseIf (FlowrateOut288 > 2.0) && (FlowrateOut288<= 2.5), !- A14
> Set OpenFactor288 = 0.8,!- A15
> Else,
> Set OpenFactor288 = null,
> Endif, !- A16
> set FlowrateIn289=FlowIn289, !- A17
> set FlowrateOut289=FlowOut289, !- A18
> If (FlowrateIn289 > 15.0),!- A4
> Set OpenFactor289 = 0,!- A5
> ElseIf (FlowrateIn289 > 3.0),!- A19
> Set OpenFactor289 = 0.7,!- A20
> ElseIf (FlowrateIn289 > 2.5) && (FlowrateIn289<= 3.0), !- A21
> Set OpenFactor289 = 0.75, !- A22
> ElseIf (FlowrateIn289 > 2.0) && (FlowrateIn289<= 2.5), !- A23
> Set OpenFactor289 = 0.8,!- A24
> ElseIf (FlowrateOut289 > 3.0), !- A25
> Set OpenFactor289 = 0.7,!- A26
> ElseIf (FlowrateOut289 > 2.5) && (FlowrateOut289<= 3.0), !- A27
> Set OpenFactor289 = 0.75, !- A28
> ElseIf (FlowrateOut289 > 2.0) && (FlowrateOut289<= 2.5), !- A29
> Set OpenFactor289 = 0.8,!- A30
> Else,
> Set OpenFactor288 = null,
> EndIf; !- A31
>
>
> !- =========== ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:GLOBALVARIABLE ===========
>
> EnergyManagementSystem:GlobalVariable,
> FlowrateIn288, !- Erl Variable 1 Name
> FlowrateOut288, !- Erl Variable 2 Name
> FlowrateIn289, !- Erl Variable 3 Name
> FlowrateOut289; !- A4
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean marais" <jeannieboef@> wrote:
> >
> > Hi Sam, I got that working nicely, but can one somehow also modulate with m3/s or ACH? I still get very hi ACH, where the occupant would close the window.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "samuel.brunswick" <samuel.brunswick@> wrote:
> > >
> > > Hi Jean,
> > >
> > > You may be seeing high ACH because your surface control is set to 'Constant'. Constant means that the window is open all the way (ie open factor = 1 or no modulation), whenver the availability schedule is non-zero. If you want the window open area to modulate based on dT you have two options. First, if you set the surface control type to 'ZoneLevel' it will modulate the window open area based on the modulation logic described in your AirflowNetwork:MultiZone:Zone object. Second, if you set the surface control type to 'Temperature' it will follow the modulation logic described in your AirflowNetwork:MultiZone:Surface object. You might have to adjust your dT's for minimum and maximum opening factors (for instance, 15degC for minimum venting factor may be a little large).
> > >
> > > It might be useful to output the open factor for the window so you can see whether it is modulating or not:
> > >
> > > Output:Variable,
> > > *, !- Key Value
> > > Window/Door Venting Opening Factor , !- Variable Name
> > > hourly; !- Reporting Frequency
> > >
> > > Hope this helps,
> > >
> > > Sam
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean marais" <jeannieboef@> wrote:
> > > >
> > > > hi All, I'm seeing large air change rates (10-20 ACH) when the outdoor temp is at 7 degC and indoor temp is at 21 degC. The "Zone" level control is set for dT of 5 degC and the "surface" level control is set for "constant". See below...please advise.
> > > >
> > > > AirflowNetwork:MultiZone:Zone,
> > > > 118129, !- Zone Name
> > > > Temperature, !- Ventilation Control Mode
> > > > 20001, !- Ventilation Control Zone Temperature Setpoint Schedule Name
> > > > 0, !- Minimum Venting Open Factor {dimensionless}
> > > > 0, !- Indoor and Outdoor Temperature Difference Lower Limit For Maximum Venting Open Factor {deltaC}
> > > > 5, !- Indoor and Outdoor Temperature Difference Upper Limit for Minimun Venting Open Factor {deltaC}
> > > > , !- Indoor and Outdoor Enthalpy Difference Lower Limit For Maximum Venting Open Factor {deltaJ/kg}
> > > > , !- Indoor and Outdoor Enthalpy Difference Upper Limit for Minimun Venting Open Factor {deltaJ/kg}
> > > > 12345; !- Venting Availability Schedule Name
> > > >
> > > > AirflowNetwork:MultiZone:Surface,
> > > > P_118129_1_0_0_0_0_0_Win,!- Surface Name
> > > > P_118129_1_0_0_0_0_0_Win,!- Leakage Component Name
> > > > P_118129_1_0_0_0_0_0_Win,!- External Node Name
> > > > 1, !- Window/Door Opening Factor, or Crack Factor {dimensionless}
> > > > Constant, !- Ventilation Control Mode
> > > > 20001, !- Ventilation Control Zone Temperature Setpoint Schedule Name
> > > > .01, !- Minimum Venting Open Factor {dimensionless}
> > > > 0, !- Indoor and Outdoor Temperature Difference Lower Limit For Maximum Venting Open Factor {deltaC}
> > > > 15, !- Indoor and Outdoor Temperature Difference Upper Limit for Minimun Venting Open Factor {deltaC}
> > > > , !- Indoor and Outdoor Enthalpy Difference Lower Limit For Maximum Venting Open Factor {deltaJ/kg}
> > > > , !- Indoor and Outdoor Enthalpy Difference Upper Limit for Minimun Venting Open Factor {deltaJ/kg}
> > > > 2; !- Venting Availability Schedule Name
> > > >
> > >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/