Re: [EnergyPlus_Support] FanPerformance:NightVentilation: nightmanager not turning fan on? Any ideas?





You are using AvailabilityManager:NightCycle. I think you should use  AvailabilityManager:NightVentilation with FanPerformance:NightVentilation.
IO Ref page 1619 (1660 absolute).
Hope this helps.
Chandan

On 8/25/2011 8:35 AM, Jean marais wrote:
 

I am trying to reduce the fan flowrate to 30% during night hours...using FanPerformance:NightVentilation

Schedule:Compact,
DOAS Supply Fan 100 Percent,
Any Number,
Through: 12/31,
For: AllDays,
Until: 05:00, 0,
Until: 22:00, 1,
Until: 24:00, 0;

Schedule:Compact,
DOAS Supply Fan 30 Percent,
Any Number,
Through: 12/31,
For: AllDays,
Until: 05:00, 1,
Until: 22:00, 0,
Until: 24:00, 1;

Fan:VariableVolume,
DOAS Supply Fan, !- Fan Name
DOAS Supply Fan 100 Percent, !- Availability Schedule Name
.7, !- Fan Efficiency
0, !- Delta Pressure {Pa}
555, !- Max Flow Rate {m3/s} 555,
Fraction, !- Min Flow Rate Input Method , FixedFlowRate
1, !- Min Flow Fraction
0, !- Min Air Flow Rate {m3/s}
1, !- Motor Efficiency
1, !- Motor in Airstream Fraction
0.35071223, !- Fan Coefficient 1
0.30850535, !- Fan Coefficient 2
-0.54137364, !- Fan Coefficient 3
0.87198823, !- Fan Coefficient 4
0, !- Fan Coefficient 5
DOAS Cooling Coil Air Outlet, !- Fan Inlet Node
DOAS Supply Fan Outlet; !- Fan Outlet Node Name

AvailabilityManagerAssignmentList,
AHU Availability Managers, !- Name
AvailabilityManager:NightCycle, !- System Availability Manager type
DOAS Availability; !- System Availability Manager name

AvailabilityManager:NightCycle,
DOAS Availability, !- Name
DOAS Supply Fan 30 Percent, !- Applicability Schedule Name
DOAS Supply Fan 100 Percent, !- Fan Schedule Name
CycleOnAny, !- Control Type
1, !- thermostat on/off tolerance {deltaC}
3600, !- Cycling run time {s}
; !- Control Zone Name

!-specifies alternative parameters for fan.
!-These alternate parameters are used when a system manager
!-(such as AvailabilityManager:NightVentilation) sets a specified flow rate for a central forced air system.
FanPerformance:NightVentilation,
DOAS Supply Fan, !- Fan Name
0.7, !- Fan Efficiency
0, !- Pressure Rise {Pa}
166.6, !- Maximum Flow Rate {m3/s} !30% of 395 = 118.5.....50% of 395 = 197.5
1, !- Motor Efficiency
1.0; !- Motor in Airstream Fraction



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___