|
Hi, The evaporator delta temperature in this case is calculated as the difference between the temperature at evaporator inlet node and temperature setpoint at evaporator outlet node. (when 'Chiller Flow Mode' = VariableFlow in the Chiller:ConstantCOP). If the delta temp is greater than zero, then that is used to calculate evap mass flow rate. EvapMassFlowRate = ABS(QEvaporator/CP/EvapDeltaTemp) If the delta temp is not greater than zero, EvapMassFlowRate is set to zero and the warning is issued. This warning is issued when the plant flow rate is not resolved. And in the latest Constant COP chiller model in EnergyPlus, this warning is removed . So I think you can ignore it. Hope this helps. Chandan On 8/30/2011 7:14 AM, Xing wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |