[EnergyPlus_Support] Primary pump and secondary pump



We have a system 8 and a primary-secondary pump system for chilled water.  We are not sure about how to use E+ to model them.  The approach we are taking now is:

1. Use the default pressure drop value in E+ and let fan power and volume flow rate be autosized, for both pumps.
2. Check the output results and get the flow rate for both pumps and they are the same.
3. Use the flow rate and apply the ASHRAE code requirement (349 kW for 1000 L/s) to get the required fan power.

At this step, we are a little confused.  This calculated fan power should be the power required for the pump SYSTEM.  How to distribute it between the two pumps?

We generated a system 8 IDF from E+ website and noted that it uses two different pressure drops for the primary pump and secondary pump and their ratio is approximately 2:1, meaning that the primary pump needs to overcome a pressure drop larger than the secondary pump.

Please help. Thanks!



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/