Hi, Xing
I thought that the Seasonal Reset Supply Air Temp Sch has some special useage therefore I did not check its values. ===================== The above was used in the follow set point manager. You are using it to set the Air Loop Outlet Node. The air to the zones are controlled to 16°C. This caused the zone mean temperature to be around 20 to 22 degtees. After I raised it to 25°C, the zone mean temperature became 27 to 28 degree C. The value should be less than the thermostat value, and higher than the heating set point value. ================= One of the reasons for using the setpoint for the AHU is to free the zone thermostat for use in the zone. The supply air is at a fixed temperature. The variable damper in each zone adjust aht amount controlled by the thermostat. When the temperature is too low with the damper at the minimum setting, the reheat heater is turned. In your system, because the damper is not a variable one, there is no minimum point to turn on the heater. Therefore, the zone temperature continue to fall. VRV, VAV with VAV diffusers are for large luxury system. It may be efficient when the location has large variation in outdoor temperature and internal load. The initial cost is high because of the added sensors and control requirement. For example, a VAV diffuser has a duct temperture sensor, a room air sensor, a control circuit driving two stepping motors (open and close) Even when the system is not running, some power is consumed. The control range is only +-two degrees from the duct temperature. VRV is achieved by using multiple stages of compressors and one small variable compressor. The step change require computer load sensing and predictuion. Therefore it is not economical for a small system. ====================== The traditional non-VAV system uses one of the zone thermostat as the AHU control thermostat. This is actually the configuration of all the current AHU with a single thermostat per AHU. The common system is one AHU connected to a duct with branches fitted with manually adjustable dampers with is adjusted once on installation. In EPlus, a fraction is asigned to each zone, with the sum total equal to one. All the zones has a thermostat, but only one of them is active and all the others are inactive, unless there is reheat and other zone equipment to be controlled. Because the theremostat is controlling the temperature of the zone, there is no error in the master zone. There is no need for the ventilation objects, if you can increase the fan volume of the AHU. Use ventilation objects, if you want to have a quick look at the natural ventilation states. ========================= You need to make a decision, on which unit you would like to use. The design procedure is usually to generate a complete IdealLoadsAirSystem first. Use different DesignDay and CustomDays to find the natural temperature of the building and the HVAC requirement. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: xing.shi.2006@xxxxxxxxx Date: Thu, 8 Sep 2011 23:33:58 +0000 Subject: [EnergyPlus_Support] Re: Why T becomes so low
Dr. Li,
Thank you again for your detailed reply! The interesting thing is that the winter zone T was maintained well as we hoped (setpoint 20 degree C during occupied hours). In summer, the zone T (from 1-k to 5-k) is kept too low. The setpoint is 26 degree C but the zone T goes down to 20. Based on the above observation and checking the SVG, it appeared that 1-k to 5-k zones are connected with the HVAC. Otherwise, what is adjusting the zone T? We will try to understand the equipment grouping advice you gave us. If you changed our IDF and got what you consider correct, would you please kindly email it to shixing_seu@xxxxxxx? For whatever reason, I cannot download attachments from this website. Many thanks! --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@...> wrote: > > > A few more points that I have observed.============Compact schedules:For: WeekendsAndAllOtherDays includes the DesignDays. Therefore my DesignDay only simulation do not see the system running. Normally, the DesignDay should be with the weekdays, unless the load is higher at the weekends. When the system is not available, the temperature setting has no effect.===============ZoneHVAC:EquipmentConnections, 1-K, !- Zone Name Zone1Equipment, !- Zone Conditioning Equipment List Name Zone1Inlets, !- Zone Air Inlet Node or NodeList Name , !- Zone Air Exhaust Node or NodeList Name Zone 1 Node, !- Zone Air Node Name Zone 1 Outlet Node; !- Zone Return Air Node Name This is where you changed the zond name. Normally, Zone1 should remain as 1-K.==========================##def ZoneHVAC_EqCn [ ZoneNM ]ZoneHVAC:EquipmentConnections, ZoneNM, !- Zone Name ZoneNM EquipmentList, !- Zone Conditioning Equipment List Name ZoneNM Air Inlet Node, !- Zone Air Inlet Node or NodeList Name , !- Zone Air Exhaust Node or NodeList Name ZoneNM Air Node, !- Zone Air Node Name ZoneNM Air Outlet Node; !- Zone Return Air Node Name##enddef=========================ZoneHVAC_EqCn [ 1-K ]ZoneHVAC_EqCn [ 2-k ]ZoneHVAC_EqCn [ 3-K ]ZoneHVAC_EqCn [ 4-K ]ZoneHVAC_EqCn [ 5-K ] Typing the above five lines in the .imf file will expended to the five objects in the .empIDF file. The people, electric, equipment list, zone equipment, etc. can all be included in the above macro list definition.============AirLoopHVAC, Typical Terminal Reheat 1, !- Name Reheat System 1 Controllers, !- Controller List Name Reheat System 1 Avail List, !- Availability Manager List Name autosize, !- Design Supply Air Flow Rate {m3/s} Air Loop Branches, !- Branch List Name , !- Connector List Name Air Loop Inlet Node, !- Supply Side Inlet Node Name Return Air Mixer Outlet, !- Demand Side Outlet Node Name Zone Equipment Inlet Node, !- Demand Side Inlet Node Names Air Loop Outlet Node; !- Supply Side Outlet Node Names > You are calling this air loop as a reheat terminal. Actually it is a system AHU [AHY1 system].The air loop branches list points to the air loop main branch which includes the OA mixer box, cooling coil and the fan. All the components in the macro should have the AHU1 as the prefix. =======I have not found the set point temperature for the AHU. Because you are using setpoint control for the coil, the zone thermostat is not used directly. I shall try to re group your file to trace the air loop controllers and the cooling coil controller, and the controller MixedAir. Dr. Li > To: EnergyPlus_Support@xxxxxxxxxxxxxxx > From: xing.shi.2006@... > Date: Wed, 7 Sep 2011 23:58:24 +0000 > Subject: [EnergyPlus_Support] Re: Why T becomes so low > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Dr. Li, thanks! > > > > We checked the SVG diagram and it seemed to be correct. In our configuration, only 5 big zones (from 1-k to 5-k) are conditioned spaces. > > > > The shading of the basement is a minor thing because the basement wall has some little spaces outside that are digged down to provide natural lighting. > > > > By the way, for some reason, I cannot download the error file you uploaded. > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@> wrote: > > > > > > > > > Hi, HanSin I had simulated your IDF and had a quick look at the result. The error file is attached. The simulation configuration is not correct. The five fan coils in the air loop are not connected to any zones. Zone 1 to zone 5 do not exist in you IDF. You have infiltration in all zones. The zone temperature is simply flowing the outside air temperature and regulated by the ground temperature. There is no zone heating or cooling load. Zone -1-T seems to in the basement. There are errors on shading. If -1-T is a basement, then all the shading on the windows are very strange arrangement. I cannot tell exactly, because your z in the zone origin is 3.5 and the z in the floor is -7. I always use one origin for the building input. > > > > > > Dr. Li > > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx > > > From: xing.shi.2006@ > > > Date: Wed, 7 Sep 2011 18:35:36 +0800 > > > Subject: [EnergyPlus_Support] Why T becomes so low > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Attached is our IDF file. It is a 5-story building with two chillers for cooling and electric heating. The srange thing is that the simulation shows that the zone T is well controlled as the schedule defines in winter (20 degree C). However, in summer the schedule wants to maintain the zone T at 26 degree C but the output shows that the T overshoots to 20 degree C. > > > We replaced the HVAC system with IdealSystem and the zone T is well controlled. I guess this means that the schedule has no error. We have been working on this problem for several days and are really puzzled. > > > Please help. Thanks! XS > > > > __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |