Hi Dr. Li,
I find the "environment tank" analogy very interesting. Particularly, that the relief air is equal to the ODA flowing into the ODA system. In real life as in the simulation more than 1 system may be present, e.g. AHU serves supply air to both office and kitchen zones, but the kitchen has it's own fan:zoneexhaust to the outdoors.
In this case the relief air of the AHU is not equal to the supply air, but the "environment tank" remains balanced as the kitchen also exhausts to it.
Now when kitchen makeup air is the combination of supply air and infiltrated via the office zones, it becomes tricky. As the demands of the kitchen and the offices are independant, it may occure that the flow is unbalanced at any possible timepoint. Should one not wish to use an AFN crack between kitchen and office and office and outdoors, is there a way you would suggest to address the unbalanced flow?
e+ simply issues the warning that the unbalanced air is not flowing in from outdoors and may decrease the accuracy of results.
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/