[EnergyPlus_Support] Re: Thickness of the wall
Dear Niraj
You can check it by yourself!
1.- Look at the *.eio file once a simulation have been run.
2.- Search the term"Zone information", and carefully spot the adequate input, in this case "Volume (m3)", so look at the 18th number in the list (I reccomemd to print it and examinate the raw data carefully.
3.- In the below example Volume is 3121.36 m3, (It's easy to find as it is the inmediate before of "TARP"...but as I said, do locate the appropriate value carefully).
Whatever your input may be, that's the volume e+ is considering for a certain zone.
----------------------------------------------------------------------
Example
! <Zone Information>,Zone Name,North Axis {deg},Origin X-Coordinate {m},Origin Y-Coordinate {m},Origin Z-Coordinate {m},Centroid X-Coordinate {m},Centroid Y-Coordinate {m},Centroid Z-Coordinate {m},Type,Zone Multiplier,Zone List Multiplier,Minimum X {m},Maximum X {m},Minimum Y {m},Maximum Y {m},Minimum Z {m},Maximum Z {m},Ceiling Height {m},Volume {m3},Zone Inside Convection Algorithm {Simple-Detailed-CeilingDiffuser-TrombeWall},Zone Outside Convection Algorithm {Simple-Detailed-Tarp-MoWitt-DOE-2-BLAST}, Floor Area {m2},Exterior Gross Wall Area {m2},Exterior Net Wall Area {m2},Exterior Window Area {m2}, Number of Surfaces, Number of SubSurfaces, Number of Shading SubSurfaces, Part of Total Building Area
Zone Information, ZONE1,0.0,0.00,0.00,0.00,11.14,21.90,1.60,1,1,1,0.00,22.27,0.00,43.80,0.00,3.20,3.20,3121.36,TARP,DOE-2,975.43,422.85,364.62,46.81,6,25,0,Yes
----------------------------------------------------------------------
Yours.
Luis Blanes
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Niraj Poudel" <nirajpoudel@...> wrote:
>
> Dear Energyplus users,
>
> When I create a 3 foot by 3 foot box in OpenStudio and in the EnergyPlus Idf editor create a say, 10 cm thick wall for each surface of the box. Where is the wall created? As in,
>
> a) Is the air volume inside 3 X 3 X3 = 9 Ft cubed
>
> OR
>
> b) The inside volume is 2.9 X 2.9 X 2.9 = 24.39 Ft cubed?
>
> OR
>
> c) The inside air volume is 2.95 X 2.95 X 2.95 = 25.67 ft cubed? (Assuming the walls are build right in the middle)
>
> I look forward to hearing from you guys at your earliest of convenience.
>
> Sincerely yours'
> Niraj Poudel
> Clemson University
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/