Re: [EnergyPlus_Support] Have a question for the output: Meter





Meters for xxx -- is the name of a variable that is on the following displayed meters.

you would output the meter by Output:Meter, Electricity:HVAC ---

If you want only the value of that fan, you would put in:

Output:Variable, 12796,AHU-1-4TH FLOOR AHU SUPPLY FAN:Fan Electric Consumption, hourly;


At 09:04 PM 10/3/2011, Ke Xu wrote:
Hi, all,
I am modeling a building that is served by several AHUs, and I want E+ outputs AHU supply fan hourly electricity consumption. I pasted a sample meter for a AHU supply fan found in the .mtd file:
" Meters for 12796,AHU-1-4TH FLOOR AHU SUPPLY FAN:Fan Electric Consumption [J]
  _OnMeter_=Electricity:Facility [J]
  _OnMeter_=Electricity:HVAC [J]
  _OnMeter_=Fans:Electricity [J]
  _OnMeter_=General:Fans:Electricity [J]"

I inserted the following terms into the .idf file, but it doesn't work.
"Output:Meter,
 12796,AHU-1-4TH FLOOR AHU SUPPLY FAN:Fan Electric Consumption,  !- Name
 Hourly;                 !- Reporting Frequency"

Can anyone here tell me how I can compose the "output:meter" object to get the correct fan energy consumed by the AHU supply fan above?

Thanks.

Ke



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___