[EnergyPlus_Support] Re: Solar Distribution



Thanks Pedro,

When beam solar strikes a surface, my understanding is that the reflected component is diffused and the diffused solar is shared evenly amongst other surfaces withion the zone. I assume the diffuse reflected solar also transmits through any internal glazing?

Also, how is solar reflected by the internal blind treated? The inputoutput reference suggests that it is reflected as diffuse. if this is the case, how is the diffuse reflected solar shared amongst other surfaces within the zone? Is it shared evenly amongst all surfaces as well?

Regards,

Dan



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Pedro Peixeiro <ppeixeiro@...> wrote:
>
> Dan,
> 
> The radiation that eventually passes through the blind is transmitted 
> through the interior window. You can use the output "beam solar 
> transmitted through interior window" in order to evaluate this.
> 
> Pedro.
> 
> On 13-10-2011 8:27, dan_grunbaum wrote:
> >
> > Hi there
> >
> > I'm attempting to model a ventilated double skin facade by creating a 
> > cavity zone 1000mm deep adjacent to the occupied (perimeter) zone. The 
> > external surface of the cavity is glazed and the internal surface 
> > seperating the cavity from the perimeter zone is also glazed and there 
> > is an operable blind within the cavity.
> >
> > We are currently using the FullExteriorandInteriorwithReflections 
> > solar distribution model. From documentation in the inputoutput 
> > reference we can see that solar transmitted through the external 
> > window is traced and then EnergyPlus calculates the amount of beam 
> > radiation falling on each surface in the cavity zone, including floor, 
> > walls and windows. However it is not clear in the inputoutput 
> > reference what happens to radiation that falls on the internal window 
> > seperating the cavity and perimeter zone.
> >
> > Can someone confirm that the beam radiation is transmitted through the 
> > internal window into the perimeter zone?
> >
> > Thanks,
> > Dan
> >
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/