Re: [EnergyPlus_Support] Help me to create the VAV system and zone





Not sure it the rest of you HVACTemplates got cut of in my email but you also need a HVACTemplate:System:VAV object to complete the HVAC system. See example file HVACTemplate-5ZoneVAV* or Excercise2B( or 2C)-Solution.idf for examples. You just wont need all the HVACTemplate:Zone:VAV object except for 1.


On 10/13/2011 10:42 AM, xav31sob wrote:
 

Hey,

I need your help. I would like to incorporate in one room the VAV HVAC template. But it doesn't work.

In the IDF file I have this :

where
Block1:Meetingroom et the room where I need the heating and cooling,

If you have any idea, it's my first time on energplus.
Thx

!- =========== ALL OBJECTS IN CLASS: ZONECONTROL:THERMOSTAT ===========

ZoneControl:Thermostat,
Block1:Meetingroom, !- Name
Block1:Meetingroom, !- Zone or ZoneList Name
Zone Control Type Sched, !- Control Type Schedule Name
ThermostatSetpoint:DualSetpoint, !- Control 1 Object Type
DualSetPoint; !- Control 1 Name

!- =========== ALL OBJECTS IN CLASS: THERMOSTATSETPOINT:DUALSETPOINT ===========

ThermostatSetpoint:DualSetpoint,
DualSetPoint, !- Name
Block1:Meetingroom Heating SP Sch, !- Heating Setpoint Temperature Schedule Name
Block1:Meetingroom Cooling SP Sch; !- Cooling Setpoint Temperature Schedule Name

!- =========== ALL OBJECTS IN CLASS: HVACTEMPLATE:ZONE:VAV ===========

HVACTemplate:Zone:VAV,
Block1:Meetingroom, !- Zone Name
VAVSystem, !- Template VAV System Name
DualSetPoint, !- Template Thermostat Name
autosize, !- Supply Air Maximum Flow Rate {m3/s}
, !- Zone Heating Sizing Factor
, !- Zone Cooling Sizing Factor
Constant, !- Zone Minimum Air Flow Input Method
, !- Constant Minimum Air Flow Fraction
, !- Fixed Minimum Air Flow Rate {m3/s}
, !- Minimum Air Flow Fraction Schedule Name
Flow/Person, !- Outdoor Air Method
, !- Outdoor Air Flow Rate per Person {m3/s}
, !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
, !- Outdoor Air Flow Rate per Zone {m3/s}
HotWater, !- Reheat Coil Type
, !- Reheat Coil Availability Schedule Name
Reverse, !- Damper Heating Action
, !- Maximum Flow per Zone Floor Area During Reheat {m3/s-m2}
, !- Maximum Flow Fraction During Reheat
, !- Maximum Reheat Air Temperature {C}
, !- Design Specification Outdoor Air Object Name
, !- Supply Plenum Name
, !- Return Plenum Name
HotWater, !- Baseboard Heating Type
Block1:Meetingroom Heating Availability Sch, !- Baseboard Heating Availability Schedule Name
autosize; !- Baseboard Heating Capacity {W}


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___