Thanks for the help

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Dru Crawley <dbcrawley@...> wrote:
>
> The MacroData sets are located in C:\EnergyPlusV6-0-0\MacroDataSets.
> 
> Open the Locations-DesignDays.xls.  Then click on the WMO06 Europe tab, and
> then Europe_wmo_region_6_design_days link.  That will open a .ZIP file
> containing the input macro file (IMF) for design conditions in Europe.  The
> locations that you highlighted on the map will have design conditions listed
> then in .IDF format similar to the .DDY.  Open the .IMF in a text editor.
> 
> For example, Cardiff Airport is shown as:
> 
> ##ifdef GBR_CARDIFF-WALES_ARPT
>  Site:Location,
>    Cardiff Wales Arpt GBR WMO=37150,     !- Location Name
>       51.40,     !- Latitude {N+ S-}
>       -3.35,     !- Longitude {W- E+}
>        0.00,     !- Time Zone Relative to GMT {GMT+/-}
>       67.00;     !- Elevation {m}
> 
>  !  WMO=37150 Time Zone=GMT        (GMT) Greenwich Mean Time : Dublin,
> Edinburgh, Lisbon, London
>  !  Data Source=ASHRAE 2009 Annual Design Conditions
>  RunPeriodControl:DaylightSavingTime,
>    Last Sunday in March,    !- StartDate
>    Last Sunday in October;    !- EndDate
> 
>  ! Using Design Conditions from "Climate Design Data 2009 ASHRAE Handbook"
>  ! Cardiff Wales Arpt GBR Extreme Annual Wind Speeds, 1%=13.3m/s,
> 2.5%=11.7m/s, 5%=10.3m/s
>  ! Cardiff Wales Arpt GBR Extreme Annual Temperatures, Max Drybulb=-5.3°C
> Min Drybulb=27.7°C
> 
>  ! Cardiff Wales Arpt GBR Annual Heating Design Conditions Wind Speed=5.2m/s
> Wind Dir=60
>  ! Coldest Month=February
>  ! Cardiff Wales Arpt GBR Annual Heating 99.6%, MaxDB=-3°C
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Htg 99.6% Condns DB,     !- Name
>          -3,      !- Max Dry-Bulb {C}
>         0.0,      !- Daily Temp Range {C}
>          -3,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         5.2,      !- Wind Speed {m/s} design conditions vs. traditional 6.71
> m/s (15 mph)
>          60,      !- Wind Direction {Degrees; N=0, S=180}
>        0.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           2,      !- Month
>   WinterDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Wetbulb;      !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Heating 99%, MaxDB=-1.5°C
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Htg 99% Condns DB,     !- Name
>        -1.5,      !- Max Dry-Bulb {C}
>         0.0,      !- Daily Temp Range {C}
>        -1.5,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         5.2,      !- Wind Speed {m/s} design conditions vs. traditional 6.71
> m/s (15 mph)
>          60,      !- Wind Direction {Degrees; N=0, S=180}
>        0.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           2,      !- Month
>   WinterDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Wetbulb;      !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Humidification 99.6% Design Conditions
> DP=>MCDB, DP=-6.8°C
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Hum_n 99.6% Condns DP=>MCDB,     !- Name
>        -1.1,      !- Max Dry-Bulb {C}
>         0.0,      !- Daily Temp Range {C}
>        -6.8,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         5.2,      !- Wind Speed {m/s} design conditions vs. traditional 6.71
> m/s (15 mph)
>          60,      !- Wind Direction {Degrees; N=0, S=180}
>        0.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           2,      !- Month
>   WinterDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Dewpoint;     !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Humidification 99% Design Conditions
> DP=>MCDB, DP=-5°C
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Hum_n 99% Condns DP=>MCDB,     !- Name
>         0.1,      !- Max Dry-Bulb {C}
>         0.0,      !- Daily Temp Range {C}
>          -5,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         5.2,      !- Wind Speed {m/s} design conditions vs. traditional 6.71
> m/s (15 mph)
>          60,      !- Wind Direction {Degrees; N=0, S=180}
>        0.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           2,      !- Month
>   WinterDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Dewpoint;     !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Heating Wind 99.6% Design Conditions
> WS=>MCDB, WS=17.6m/s
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Htg Wind 99.6% Condns WS=>MCDB,     !- Name
>           7,      !- Max Dry-Bulb {C}
>         0.0,      !- Daily Temp Range {C}
>           7,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>        17.6,      !- Wind Speed {m/s} design conditions vs. traditional 6.71
> m/s (15 mph)
>          60,      !- Wind Direction {Degrees; N=0, S=180}
>        0.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           2,      !- Month
>   WinterDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Wetbulb;      !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Heating Wind 99% Design Conditions
> WS=>MCDB, WS=14.8m/s
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Htg Wind 99% Condns WS=>MCDB,     !- Name
>         7.1,      !- Max Dry-Bulb {C}
>         0.0,      !- Daily Temp Range {C}
>         7.1,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>        14.8,      !- Wind Speed {m/s} design conditions vs. traditional 6.71
> m/s (15 mph)
>          60,      !- Wind Direction {Degrees; N=0, S=180}
>        0.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           2,      !- Month
>   WinterDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Wetbulb;      !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt Annual Cooling Design Conditions Wind Speed=4.3m/s
> Wind Dir=100
>  ! Hottest Month=July
>  ! Cardiff Wales Arpt GBR Annual Cooling (DB=>MWB) .4%, MaxDB=24.8°C
> MWB=17.9°C
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Clg .4% Condns DB=>MWB,     !- Name
>        24.8,      !- Max Dry-Bulb {C}
>         7.4,      !- Daily Temp Range {C}
>        17.9,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         4.3,      !- Wind Speed {m/s} design conditions vs. traditional 3.35
> m/s (7mph)
>         100,      !- Wind Direction {Degrees; N=0, S=180}
>        1.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           7,      !- Month
>   SummerDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Wetbulb;      !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Cooling (DB=>MWB) 1%, MaxDB=22.8°C
> MWB=17.1°C
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Clg 1% Condns DB=>MWB,     !- Name
>        22.8,      !- Max Dry-Bulb {C}
>         7.4,      !- Daily Temp Range {C}
>        17.1,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         4.3,      !- Wind Speed {m/s} design conditions vs. traditional 3.35
> m/s (7mph)
>         100,      !- Wind Direction {Degrees; N=0, S=180}
>        1.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           7,      !- Month
>   SummerDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Wetbulb;      !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Cooling (DB=>MWB) 2%, MaxDB=21.1°C
> MWB=16.4°C
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Clg 2% Condns DB=>MWB,     !- Name
>        21.1,      !- Max Dry-Bulb {C}
>         7.4,      !- Daily Temp Range {C}
>        16.4,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         4.3,      !- Wind Speed {m/s} design conditions vs. traditional 3.35
> m/s (7mph)
>         100,      !- Wind Direction {Degrees; N=0, S=180}
>        1.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           7,      !- Month
>   SummerDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Wetbulb;      !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Cooling (WB=>MDB) .4%, MDB=22.8°C WB=18.7°C
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Clg .4% Condns WB=>MDB,     !- Name
>        22.8,      !- Max Dry-Bulb {C}
>         7.4,      !- Daily Temp Range {C}
>        18.7,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         4.3,      !- Wind Speed {m/s} design conditions vs. traditional 3.35
> m/s (7mph)
>         100,      !- Wind Direction {Degrees; N=0, S=180}
>        1.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           7,      !- Month
>   SummerDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Wetbulb;      !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Cooling (WB=>MDB) 1%, MDB=21.2°C WB=17.9°C
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Clg 1% Condns WB=>MDB,     !- Name
>        21.2,      !- Max Dry-Bulb {C}
>         7.4,      !- Daily Temp Range {C}
>        17.9,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         4.3,      !- Wind Speed {m/s} design conditions vs. traditional 3.35
> m/s (7mph)
>         100,      !- Wind Direction {Degrees; N=0, S=180}
>        1.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           7,      !- Month
>   SummerDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Wetbulb;      !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Cooling (WB=>MDB) 2%, MDB=20°C WB=17.1°C
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Clg 2% Condns WB=>MDB,     !- Name
>          20,      !- Max Dry-Bulb {C}
>         7.4,      !- Daily Temp Range {C}
>        17.1,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         4.3,      !- Wind Speed {m/s} design conditions vs. traditional 3.35
> m/s (7mph)
>         100,      !- Wind Direction {Degrees; N=0, S=180}
>        1.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           7,      !- Month
>   SummerDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Wetbulb;      !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Cooling (DP=>MDB) .4%, MDB=19.9°C DP=17.2°C
> HR=0.0124
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Clg .4% Condns DP=>MDB,     !- Name
>        19.9,      !- Max Dry-Bulb {C}
>         7.4,      !- Daily Temp Range {C}
>        17.2,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         4.3,      !- Wind Speed {m/s} design conditions vs. traditional 3.35
> m/s (7mph)
>         100,      !- Wind Direction {Degrees; N=0, S=180}
>        1.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           7,      !- Month
>   SummerDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Dewpoint;     !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Cooling (DP=>MDB) 1%, MDB=19.2°C DP=16.7°C
> HR=0.0120
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Clg 1% Condns DP=>MDB,     !- Name
>        19.2,      !- Max Dry-Bulb {C}
>         7.4,      !- Daily Temp Range {C}
>        16.7,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         4.3,      !- Wind Speed {m/s} design conditions vs. traditional 3.35
> m/s (7mph)
>         100,      !- Wind Direction {Degrees; N=0, S=180}
>        1.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           7,      !- Month
>   SummerDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Dewpoint;     !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Cooling (DP=>MDB) 2%, MDB=18.3°C DP=16°C
> HR=0.0114
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Clg 2% Condns DP=>MDB,     !- Name
>        18.3,      !- Max Dry-Bulb {C}
>         7.4,      !- Daily Temp Range {C}
>          16,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         4.3,      !- Wind Speed {m/s} design conditions vs. traditional 3.35
> m/s (7mph)
>         100,      !- Wind Direction {Degrees; N=0, S=180}
>        1.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           7,      !- Month
>   SummerDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Dewpoint;     !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Cooling (Enthalpy=>MDB) .4%, MDB=23.1°C
> Enthalpy=53.4kJ/kg
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Clg .4% Condns Enth=>MDB,     !- Name
>        23.1,      !- Max Dry-Bulb {C}
>         7.4,      !- Daily Temp Range {C}
>        53.4,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         4.3,      !- Wind Speed {m/s} design conditions vs. traditional 3.35
> m/s (7mph)
>         100,      !- Wind Direction {Degrees; N=0, S=180}
>        1.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           7,      !- Month
>   SummerDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Enthalpy;      !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Cooling (Enthalpy=>MDB) 1%, MDB=21.2°C
> Enthalpy=50.5kJ/kg
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Clg 1% Condns Enth=>MDB,     !- Name
>        21.2,      !- Max Dry-Bulb {C}
>         7.4,      !- Daily Temp Range {C}
>        50.5,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         4.3,      !- Wind Speed {m/s} design conditions vs. traditional 3.35
> m/s (7mph)
>         100,      !- Wind Direction {Degrees; N=0, S=180}
>        1.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           7,      !- Month
>   SummerDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Enthalpy;      !- Humidity Indicating Type
> 
>  ! Cardiff Wales Arpt GBR Annual Cooling (Enthalpy=>MDB) 2%, MDB=19.9°C
> Enthalpy=48.2kJ/kg
>  SizingPeriod:DesignDay,
>   Cardiff Wales Arpt Ann Clg 2% Condns Enth=>MDB,     !- Name
>        19.9,      !- Max Dry-Bulb {C}
>         7.4,      !- Daily Temp Range {C}
>        48.2,      !- Humidity Indicating Condition at Max Dry-Bulb
>     100523.,      !- Barometric Pressure {Pa}
>         4.3,      !- Wind Speed {m/s} design conditions vs. traditional 3.35
> m/s (7mph)
>         100,      !- Wind Direction {Degrees; N=0, S=180}
>        1.00,      !- Clearness {0.0 to 1.1}
>           0,      !- Rain {0-no,1-yes}
>           0,      !- Snow on ground {0-no,1-yes}
>          21,      !- Day of Month
>           7,      !- Month
>   SummerDesignDay,!- Day Type
>           0,      !- Daylight Savings Time Indicator
>    Enthalpy;      !- Humidity Indicating Type
> 
> ##endif
> 
> If you copy everything between the ##Ifdef  line and the ##endif line,
> you'll have the contents of the .DDY for that location.  (This will be
> faster than waiting on me to get you the data.)
> 
> 
> 
> On Fri, Oct 14, 2011 at 11:56 AM, Mota Fernando <motabmx1@...> wrote:
> 
> > **
> >
> >
> > Dear Ms Lawrie,
> >
> > where  the macro data set from EnergyPlus can be found?
> >
> > Thanks Fernando
> >
> >  *From:* Linda Lawrie <linda@...>
> > *To:* EnergyPlus_Support@xxxxxxxxxxxxxxx
> > *Sent:* Friday, October 14, 2011 3:32 PM
> >
> > *Subject:* Re: [EnergyPlus_Support] GBR_Ebbw.Vale.Wales_MN6 weather file
> > does not contain SizingPeriod:DesignDay
> >
> >
> > The map provided shows ASHRAE design conditions that can be provided.  Not
> > weather data.
> >
> > (They are also available from the macro data set from EnergyPlus --
> > Locations/DesignDays will allow you to download a set of design days).
> >
> > At 08:27 AM 10/14/2011, Mota Fernando wrote:
> >
> >
> > Dear Mr. Crawley,<?xml:namespace prefix = o ns =
> > "urn:schemas-microsoft-com:office:office" />
> >
> >
> > Thanks for your quick replay. I have attached the map that you forwarded to
> > me with same weather files that may be closer enough to the ebbw vale file.
> > I wonder if as you mentioned in your previous e-mail, I could get them from
> > you.
> >
> > Many thanks
> >
> > Fernando
> >
> > *From:* Dru Crawley <dbcrawley@...>
> > *To:* EnergyPlus_Support@xxxxxxxxxxxxxxx
> > *Sent:* Wednesday, October 12, 2011 11:36 PM
> > *Subject:* Re: [EnergyPlus_Support] GBR_Ebbw.Vale.Wales_MN6 weather file
> > does not contain SizingPeriod:DesignDay
> >
> >
> > Unless there was design data available in the ASHRAE Handbook, the
> > Meteonorm files that we created do not have the design day objects.  Suggest
> > finding a nearby location with similar climate and elevation and use the
> > data from there.
> >
> > My knowledge of Wales topography and geography is poor -- if one of the
> > pins on the attached map look close, let me know and I'll send you the data.
> >
> >
> >
> >
> > On Wed, Oct 12, 2011 at 6:17 PM, motabmx1 <motabmx1@...> wrote:
> >
> > Dear all,
> >
> > I wonder if you can help me in the foolowing matter.
> >
> > I download from this page the file GBR_Ebbw.Vale.Wales_MN6 which I am using
> > in a project I am working at the moment. The problem is that this weather
> > file does not contain any object in the section SizingPeriod:DesignDay which
> > I think I need for sizing my HVAC, Does anyone have a file for this location
> > with the design day objects?
> >
> > thanks
> >
> > fernando
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >  
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/