We were just talking about this the other day. The defrost power is calculated as: DX Heating Coil: OutdoorCoilT = 0.82d0 * OutdoorDryBulb - 8.589d0 OutdoorCoildw = MAX(1.0d-6,(OutdoorHumRat - PsyWFnTdpPb(OutdoorCoilT,OutdoorPressure))) IF (DefrostControl .EQ. Timed) THEN FractionalDefrostTime = DefrostTime ELSE !else defrost control is on-demand FractionalDefrostTime = 1.0d0 / (1.0d0 + 0.01446d0 / OutdoorCoildw) END IF DefrostEIRTempModFac = CurveValue(DefrostEIRFT,MAX(15.555d0,InletAirWetbulbC),MAX(15.555d0,OutdoorDryBulb)) DefrostPower = DefrostEIRTempModFac * RatedTotCap/1.01667d0) * FractionalDefrostTime You want to calculate the power the HP uses while in defrost. Since the HP is in cooling mode during defrost, the DefrostEIRTempModFac performance curve should provide the cooling EIR at the defrost temperatures. The standard cooling EIR curve is a good place to start. Plot it out down to these low temperatures and see how it looks. But also notice that the RatedTotCap referred to here is the Rated Heating Capacity, not the cooling capacity. So you may have to manipulate the cooling EIR temperature curve a little to get a proper DefrostEIR function of temperature curve (since power will be CoolingEIR multiplied by heating capacity). And no, we do not a performance curve for this. Although I have seen a DOE curve used for the HP model. Note that below 15.555 C for either curve input (indoor WB or outdoor DB), the impact on the curve result due to that input is constant even if you try to reduce the limits in the curve object (i.e., see MAX argument in equation above) . This shouldn't matter much since the HP should be shutting down on low ambient temperature soon after this limit is reached. CURVE:BIQUADRATIC, HPACDefrostEIRFT, ! name,
DOE-2.1E,
COOL-EIR-FT for RESYS w/ SI temps (SDL-C11) 0.297145,
0.0430933, -0.000748766, 0.00597727, 0.000482112, -0.000956448, 15.555, 23.88889, ! extended limits 15.555 C
- 23.889 C
(60F-75F) wet bulb 15.555, 46.11111; ! extended limits 15.555 C
- 46.111 C
(60F-115F) outdoor dry bulb On 10/20/2011 7:06 AM, jvd2pe wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |