Hi. First you need to create your shading element through one of these objects: WindowMaterial:Shade or WindowMaterial:Blind (it's also possible to create a WindowMaterial:Screen, but this can only be outside the window). After, create a WindowProperty:ShadingControl object. In the "shading type" field, select the appropriate type: BetweenGlassShade or BetweenGlassBlind, depending on your previous choice. Finally, when you create your exterior window with, for example, the FenestrationSurface:Detailed object, reference the shading control object you previously created in the "shading control name" field, and you should be good to go. Pedro On 20-10-2011 20:51, nik_jap wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.