[EnergyPlus_Support] Re: Unitary System Fan Mode - Cycling/Continous
Thanks. I'll check it.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Don Shirey <dshireyiii@...> wrote:
>
> It might seem obvious, but also remember that the "Pump Control Type" needs to be set to "Intermittent".
>
> From the Input Output Reference for Pump:VariableSpeed:
>
>
> Field: Pump Control Type This is a choice field of Continuous or Intermittent. A variable speed pump is defined with maximum and minimum flow rates that are the physical limits of the device. If there is no load on the loop and the pump is operating intermittently, then the pump can shutdown. For any other condition such as the loop having a load and the pump is operating intermittently or the pump is continuously operating (regardless of the loading condition), the pump will operate and select a flow somewhere between the minimum and maximum limits. In these cases where the pump is running, it will try to meet the flow request made by demand side components.
>
>
> From: Jean marais <jeannieboef@...>
> >To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> >Sent: Monday, October 31, 2011 10:17 AM
> >Subject: [EnergyPlus_Support] Re: Unitary System Fan Mode - Cycling/Continous
> >
> >
> >
> >Thanks Richard,
> >I was worried that the Unitary Unit would place a Setpoint on a node, without telling me.
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/