[EnergyPlus_Support] Re: Disable a DX coil below "xx" temp



Easy see. You've probably spent too much time avoiding EMS. Guess I don't need to send you the code. Two points: Where you have ELSE,
SET abc = Null, I would have used = 1. Null is no action, which I believe means that it will use the schedule value that you have set up in your schedule object. Correct, but I'm used to the idea that a variable will retain it's value. In this case e+ is actually changing the variable back to 1 by reading from the schedule as normal and assigning it to the variable. I just prefer to be really sure and make this a habit. The second point is that there is a verbose command which produces an .edd file where one can see 1) all the available actuators and 2) stepwise calculation of the program line for line. A good debugging tool. 

I last used EMS to setup a DCV system with VAV dampers on a DOAS my monitoring CO2 levels in zones (the current e+ system could only do this by using the mixing box not applicable to DOAS), along with a outdoor temperature dependant zone air setpoint schedule (which is actually standard practise here). 



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/