Re: [EnergyPlus_Support] CAV with VAV





Bryce,

this setup should be possible. Start with this:

For packaged variable air volume systems using direct-expansion cooling include:
HVACTemplate:Thermostat
HVACTemplate:Zone:VAV:FanPowered  (one per zone)
HVACTemplate:System:PackagedVAV   (one per AHU)
HVACTemplate:Plant:HotWaterLoop (if HW Reheat Coils are used)
HVACTemplate:Plant:Boiler (If HW Reheat Coils are used)

this will give you a variable volume dx system with parallel or series fan powered vavs at the zone level

run this simulation... EnergyPlus will create an input file with the HVACTemplates expanded out into their component objects. This file has the type '.expidf'

Rename this file to be Filename_exp.idf

Now you have the expanded HVACTemplate file which you can modify like any other EnergyPlus input data file.

Now Remove the Fan:VariableVolume object for the AHU Supply Fan and replace it with a Fan:ConstantVolume one

Also be sure to change the minimum system air flow ratio in the 'Sizing:System' object to 1.0

be sure to search the file for any instances of Fan:VariableVolume and replace them with Fan:ConstantVolume. This also occurs in the main branch of the AHU.

Hope this helps.

Jason


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___