I do not have the ASHRAE document and has not used eQuest. I have never generated ASHRAE compliance model by using Example File Generator. So I do not know what is your problem with the numbers.
As far as I gather from the users, EPlus can do more than eQuest. Unfortunately, more features also mean more difficult to use them correctly by a user. ======================= The temperature you set in the Compact schedule is up to you to choose. There are certain rules, such as the heating setpoint must not be higher than the cooling setpoint in Type4 thermostat control type, dual control with dead band. There is a whole list of ASHRAE schedules in the schedules.idf in the DataSet folder. I never use them. Sizing set point is for the EPlus to run with miniminum input values from the user. The 20°C and 24°C values in the template are for convenience and practical usage. If you want to follow any guidelines, you can changed them. Zone and system sizing objects are there for you to enter customed values. You can change them. "So my doubt is that the Object Zone:Sizing temp and Compact schedule Temp shouldn't be same? If i do so my energy consumption incresed exponentially" :( Could you please guide me on this:) The temperature in the zone sizing object are suggested limits to be used. They are not actual zone temperatures to be used in HVAC operation. Energy consumption never increase exponentially unless you make it so. =====================
Cool the supply air down to 12.65°C and then heat it up to 24°C in a zone, with a 50KW electric heater. =========================
12.65° is the usual chiller temperature. 16.7°C is the lower limit for heating supply air when the zone is occupied, commonly used cooling coil temperature for desired humididity level in the zone.
14°C and 40°C are the limites for a building when temperature control must be applied. Winter turn on some heater. Summer open some windows. In practice, all these numbers are set by the user based on their requirements. Simulation need not be real.
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: eee.javed@xxxxxxxxx Date: Mon, 7 Nov 2011 13:06:42 +0000 Subject: [EnergyPlus_Support] ASHRAE Supply Air Temp_Example file generator
Hi,
I have a very basic question and my doubt has arisen because i have used eQuest on some of the projects for ASHRAE code compliance. I have generated ASHRAE compliance model by using Example File Generator. I have following doubts: 1. Can i use the EEFG file Temperature set point directly for ASHRAE Code compliance (mainly System and Zone level). 2. I have noticed that the temperature defined at Object System:Sizing Zone:Sizing are approx. same. but the zone level Temp set point defined in Compact Schedule are OK i.e. 22 deg C and 24 deg C. So my doubt is that the Object Zone:Sizing temp and Compact schedule Temp shouldn't be same? If i do so my energy consumption incresed exponentially :( Could you please guide me on this:) Equest Supply Air Temp System Level Cooling Supply Air Temp Heating Supply Air Temp 12.65 Deg C (55F) 28 Deg C (95F) Zone Level 23.8 Deg C (75F) 21 Deg C (72F) Energy Plus Supply Air Temp from EEFG System Level Cooling Supply Air Temp Heating Supply Air Temp 12.65 Deg C 16.7 Deg C Zone Level 14.00 Deg C 40 Deg C I will love to get some feedback from Dr Li. Thanks, Regards __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.