p.s., Cooling capacity will be ~ Power input x EER
The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Karen Walkerman
Sent: Friday, November 11, 2011 12:00 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] "Heat Absorption" in Water to Water HP
That is kind of what I thought it was - usually this is roughly equivalent to the grid energy (usually electricity) used to power the machine. If you have a 5KW machine, then either the system or surrounding space needs to absorb 5KW. If the load side absorbs the heat, this is considered part of the total heating capacity of the machine, right?
Unfortunately, this is not a number given by the manufacturer of the heat pump I'm currently modeling. What is a reasonable range for absorption versus reject to the space?
I assume that this absorption is absorption into the load water loop??
Thanks!
Karen
On Fri, Nov 11, 2011 at 11:50 AM, Pregas Srinivasan <pregas@xxxxxxxxx> wrote:
Water to water HP - Geothermal water loop removes the condenser heat rejected in summer. This heat is rejected to ground. In winter the water loop absorbs heat from ground and air stream gets heated in heat pump. How much of heat absorbed is given by HP unit selection and varies between unit manufacturers.
Let me know if this helps.
PS
On Fri, Nov 11, 2011 at 11:11 AM, Karen Walkerman <kwalkerman@xxxxxxxxx> wrote:
Hi,
In the document "WaterWater_PE_Heating.xls" (available on the helpdesk) can anyone shed a little light on what "heat absorption" (column G) means?
Thanks,
Karen
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___