RE: [EnergyPlus_Support] Re: IDF Review for no Cooling





You can set a wider dead band for the un-occupied period.
 
Heating set point must be lower than the cooling set point, so that they do not overlap.
 
The dead band may be as little as 0.1°F.
 
Otherwice, you can set them to any temperature.  If I wanted to turn off the cooling completely, I simply set the cooling set point to 98°F for that zone.
 
If you have water system, you may still need the seasonal control for the plants., so that the water system will be freeze.

 Dr. Li  

 

To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: matthew.sverre.anderson@xxxxxxxxx
Date: Mon, 14 Nov 2011 18:39:01 +0000
Subject: [EnergyPlus_Support] Re: IDF Review for no Cooling

 
So do something like set a cooling set point to 74, Heating to 70 for a mean set point of 72 with a 2 degree deadband?

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean marais" <jeannieboef@...> wrote:
>
> HEATING COOLING SETPOINTS is the schedule name for both your heating setpoint and your cooling setpoint. I recommend using 2 seperate schedules to achieve a dead band.
>




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___