[EnergyPlus_Support] CoolingCoil Sizing Error





Hi!
I'm simulating an air system that consist of a heating coil, a cooling Coil,a humidifier and a reheat coil.
This is the error I really can't solve:
 
   ** Warning ** In calculating the design coil UA for Coil:Cooling:Water MAIN COOLING COIL 2
   **   ~~~   ** no apparatus dew-point can be found for the initial entering and leaving conditions;
   **   ~~~   ** the apparatus dew-point is below the coil design inlet water temperature;
   **   ~~~   ** the coil bypass factor is unrealistically large;
   **   ~~~   ** the coil outlet design conditions will be changed to correct the problem.
   **   ~~~   ** The initial design conditions are: Tair,in = 31.7000
   **   ~~~   **                                    Wair,in = 1.000000E-005
   **   ~~~   **                                    Twater,in = 7.0000
   **   ~~~   **                                    Tair,out = 20.0000
   **   ~~~   **                                    Wair,out = 5.000000E-006
   **   ~~~   ** The revised design conditions are: Tair,out = 20.0000
   **   ~~~   **                                    Wair,out = -9.000000E-005
 
Is there anybody who as an idea?!?!
Thank you!


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___