Re: [EnergyPlus_Support] Plant loop flow rate autosized to a negative number





This looks like you had set the pump to the autosize value (-99999) but hadn't put in some Sizing:* objects to make things autosize.

At 08:34 AM 11/29/2011, robdombrosky wrote:
What does it mean when a plant loop flow rate is autosized to a negative number? What should be the very origin of that problem, so I can fix it?

Thanks!


Error messages afterm simulation:

** Warning ** SizePlantLoop: Calculated Plant Sizing Design Volume Flow Rate=[-99998.49] is too small. Set to 0.0
   **   ~~~   ** ..occurs for PlantLoop=CIRCUITO AGUA CHILLED WATER LOOP
   ** Warning ** SizePump: Calculated Pump Nominal Volume Flow Rate=
[-99998.49] is too small. Set to 0.0
   **   ~~~   ** ..occurs for Pump=CIRCUITO AGUA CHW SECONDARY PUMP