[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: SetpointManager:MixedAir and Economizer question





Your missing the point. Use a set point manager to put a set point on some air node in your simulation that will not be used for control. This is a reference node set point. Then, if you want to adjust that set point, say to account for fan heat because the fan is after your coil, use a mixed air set point manager to adjust the reference node set point temperature for fan heat and place this new calculated set point at some other node. What other node? Probably the outlet of a cooling coil because for some system types, they need to be controlled by a set point.

I'm signing off for the year...Happy Holidays.

On 12/1/2011 3:47 PM, Jean marais wrote:
 

Sorry, the connection dropped out on mid post. Here is my last post again.

On a coil outlet? Coils usually need setpoints on the outlets for the controlers. This would give me a SetpointManager conflict! The exit of the mixingbox would make more sense to me.

Also, if I assign a setpoint to the fan inlet (for a blow through config.), I would set it to equal room air exhaust temp, say 22 deg for both heating and cooling modes. But I feel this is a "looser" control, because the air will be "preconditioned" with ODA mixing always to 22 deg, even if it would be more advantages if it were closer to the best achievable delivery air temperature. I guess this I a gap between theory and practise. In practise it may well be the case that the return air temperature is monitored and mixed with ODA as appropriate to achieve a mixed air temperature of roughly 22 degC after the mixing box (with taking onto account fan heat).

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> The reference node must have a setpoint assigned to it by another
> setpoint manager.
>
> Of course it does, that's why it's called a reference. Use a different
> type of set point manager to put a set point on a node (remember, the
> fan inlet node, return node, etc.). Then used the mixed air set point
> manager to read the reference node set point, adjust for fan heat, and
> place a new set point anywhere you need it (usually at a coil outlet node).
>
>
> On 12/1/2011 1:43 PM, Jean marais wrote:
> >
> > After reading the io Ref. your suggestion did not make much sense. I
> > applied it anyway and got the errors that I thought I would get.
> >
> > The reference node must have a setpoint assigned to it by another
> > setpoint manager.
> >
> > The setpoint nodes are all the nodes to which the
> > SetpointManager:MixedAir will assign the new calculated setpoint to.
> >
> > This means the Reference Node should have a setpoint assigned by
> > another manager = air delivery temperature (which should change for
> > the heating and cooling case), as this is the setpoint which you are
> > trying to hit.
> >
> > And none of the nodes in the SetpointNodeList may be set by other
> > setpointmanagers as they will conflict.
> >
> > In my current configuration I have Mixingbox,[Fan,dx cooling coil],hot
> > water coil. With setpoint managers for cooling at the dx outlet node
> > (12°C) and at the heating coil outlet (-99 to 34°C). The Setpoint
> > assigned at the exit of my htg coil doubles as my delivery air
> > setpoint temp and serves as the reference node for the
> > SetpointManager:MixedAir. My SetpointManager:MixedAir Setpoint is only
> > assigned to the exit of the Mixing box (but could also be assigned to
> > the exit of the fan.)
> >
> > I think James and I understand this object differently.
> >
> > Pointers? Comments?
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > <RRaustad@> wrote:
> > >
> > > 1) put the reference node on any node that will not be controlled, use
> > > the return node if you have to, or the fan outlet would also work
> > > 2) don't worry about upstream and downstream, just enter the fan
> > > inlet/outlet node names and the manager will do the rest
> > >
> > > What you are basically doing is calculating a set point at the
> > reference
> > > node, and then using the mixed air manager to adjust that calculated
> > set
> > > point by the fan heat. So when all is said and done, the outlet of the
> > > air loop is at the same temperature as the reference node set point
> > > temperature
> > >
> > > On 11/29/2011 11:50 AM, Jean marais wrote:
> > > >
> > > > Thanks James. A few more questions, if you'll indulge me...
> > > >
> > > > The referance node:
> > > > I assume one must be quite careful as to what setpoint is used on the
> > > > reference node (usually the last node on the supply side). For
> > > > example, if my last componant is a heating coil, I can't assign a
> > > > fixed schedule 32degC with a setpoint manager on the htg coil exit
> > > > node, if I plan heating and cooling all year round. I need to use, in
> > > > this case a setpoint manager that can decrease the setpoint on this
> > > > node during times of cooling. Right?
> > > >
> > > > The other setpoint nodes in the list:
> > > > How does the MixedAirSPmanager "know" on which node the fan sits, to
> > > > deturmine upstream and down stream from it? I don't have it here. Is
> > > > it an input field? I ask, because not just the fan takes or adds to
> > > > the air stream. Maybe, it just looks at the setpoint on each node in
> > > > the list (not the airstream temp), checks if it must be applied (eg.
> > > > clg sp not applied if in heating mode), and estimates the energy put
> > > > in or out at these nodes. Using this information, it sets the
> > setpoint
> > > > at the exit of the mixing box, then the controller tries to control
> > > > the damper to match. Right?
> > > >
> > > > Please explain "exception 1". My guess is that if the downstream htg
> > > > coil exit node was included, the manager would see it as a second fan
> > > > and (if outside had cold air) possibly introduce more than nessecary
> > > > ODA, which the poor htg coil would have to heat up. This all becomes
> > > > hellishly complicated considering econimizers and other factors.
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___