It would be nice to have a defect file that shows this. I know you have
provided many examples, but those get lost in all the tickets. Maybe E+
doesn't correctly model DX cooling coils with high OA fractions (not
sure why this would happen, we've had this discussion), or maybe the
inputs are causing problems (i.e., sizing objects). Not a defect file
with 100 zones, but one that is easy to run, report, and diagnose would
be ideal (5 zones?).
Lesson #2: EnergyPlus does not like to autosize systems with large
outdoor air loads
EnergyPlus imposed its built-in flow / capacity limits and it reduced
the coil size for several zones in order to meet the limits. Those
down-sized DX coils failed to adequately cool the zones they served ?
and unmet loads resulted.
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/