At least one issue is the current weather files seldom have reliable precipitation data. Typically a snow melt system remains on in larger installations because
it takes too long to heat the slab and ground if it is only turned on for a snow event. The new systems have a low output standby heat setting with moisture sensors to trigger high output snow melting.
Ned Lyon, P.E. (MA) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Karen Walkerman Has anyone used EnergyPlus to model snowmelt? Snow-melting is mentioned under "GroundHeatExchanger:Surface", but I am skeptical about actually using this object to melt snow. Does this object model the additional heat lost from the surface
in order to melt snow? Does it model the insulating properties of the snow if the slab is not warm enough to melt the snow? I'm looking for any feedback, ideas or discussion. Thanks! -- Karen __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.